[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] about the cooling tower
It is difficult to say for sure without seeing the input file. This type of
error usually occurs when the loop is unable to conserve mass flow around the
loop. Check the flow rates specified for the cooling tower(s) and the
condenser loop pump and in the condenser loop object. Check if there is a
bypass. Check the pump controls. Check the ACTIVE/PASSIVE settings on the
branches. See ExampleFiles\CoolingTower.idf for an example.
Mike
On 7 Dec 2006 at 10:35, dreamerfish8146 wrote:
> Dear all:
> The system of this simulation is fancoil.There are three water
> cooled chillers and three cooling towers.One condenser pump in the
> supply side.The chiller branch is composed of a chiller and a cw
> pump.In winter, purchased heating is used.There are many warnings in
> the .err file which is
> ** Warning ** COOLING TOWER:SINGLE SPEED- "TOWER1":
> ** ~~~ ** Condenser Minimum Loop Mass Flow is greater than
> Condenser Maximum Loop Mass Flow
> ** ~~~ ** Minimum Loop Mass Flow has been reset to Maximum Loop
> Mass Flow
> I changed all the related parameters to autosize but there is no
> change.Is there something wrong about the water loop? Or the parameters
> are wrong?
> Thanks for help!
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/