[EnergyPlus_Support] Constant Deck and Supply Temperatures
I am trying to simulate a 100% outside air, constant volume, constant
temperature ventilation system. I want to dehumidify the ventilation
air by using a DX coil (I used a DXSystem:AirLoop object) and then a
gas reheat coil (FURNACE:BLOWTHRU:HEATONLY). I want the air to come
off the DX coil at a maximum and constant 55F (except during the
winter when the OA to the system will be lower than that temp). I
want the air to come off the gas coil in the furnace at a contant 68F,
year round, no matter what. How do I do this?
I have tried using setpoint controllers at the outlet nodes to both
coils, but the furnace mandates that the thermostat location be in a
zone, which causes my setpoint managers to be over riden by the zone
needs.
Thanks,
Andrew
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/