Re: [EnergyPlus_Support] Constant Deck and Supply Temperatures



While the DX coil cannot control itself directly, a gas heating coil can.  For 
this application, delete the FURNACE object and put the gas heating coil 
directly on the branch and specify the coil outlet node to be the Coil Temp 
Setpoint Node.  Use SET POINT MANAGER:SCHEDULED to place the heating and 
cooling setpoints at the respective outlet nodes.

I have made a note to make sure that the I/O ref explains which coils can go 
directly on a branch, which need a controller, and which need to be contained 
inside a parent object.

Mike
  

On 7 Dec 2006 at 20:55, asheaffe wrote:

> I am trying to simulate a 100% outside air, constant volume, constant 
> temperature ventilation system.  I want to dehumidify the ventilation 
> air by using a DX coil (I used a DXSystem:AirLoop object) and then a 
> gas reheat coil (FURNACE:BLOWTHRU:HEATONLY).  I want the air to come 
> off the DX coil at a maximum and constant 55F (except during the 
> winter when the OA to the system will be lower than that temp).  I 
> want the air to come off the gas coil in the furnace at a contant 68F, 
> year round, no matter what.  How do I do this?  
> 
> I have tried using setpoint controllers at the outlet nodes to both 
> coils, but the furnace mandates that the thermostat location be in a 
> zone, which causes my setpoint managers to be over riden by the zone 
> needs.
> 
> Thanks,
> 
> Andrew
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/