Re: [EnergyPlus_Support] A question about purchased chilled and hot water
Your understanding is correct. If you are trying to take the reported purchsed
cooling/heating energy and convert is to equivalent electricity or gas, you
must divide by the average efficiency of the equipment at the district plant.
There is no assumed efficiency included in the purchased reporting. To
confirm, this, you should find that the purchased cooling energy is equal to
the sum of the chilled water coil loads plus the chilled water pump heat.
Mike
On 15 Jan 2007 at 13:14, Zhen Tian wrote:
> Dear All,
>
> I have a question about the energy use of purchased chilled and hot water. When I use purchased chilled and hot was as the plant. I got the energy use data from Report meter/ Cooling:purchased cooling and Heating: purchased heating. I am not sure about the energy use reported is energy end use or not.
>
> Based on my understanding, I guess the energy use reported here is the chilled water and hot water energy use, not the energy end use. For example, the reported annual Cooling:purchased cooling is 60GJ and Heating: purchased heating is 100 GJ. If we assume the chiller COP is 3 and boiler efficiency is 80%, then the electricity use for cooling should be 60J/3=20 GJ and natural gas energy use for boiler is 100J/0.8=125 GJ. I am wondering weather this method is correct or not?
>
> Because I have to calculate the CO2 emission based on different energy sources, I have to convert the purchased chilled and hot water to energy end uses.
>
> Thank you very much for your advices.
>
> Regards,
>
> Zhen
>
>
>
>
> ---------------------------------
> Need Mail bonding?
> Go to the Yahoo! Mail Q&A for great tips from Yahoo! Answers users.
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/