There are many REPORT VARIABLEs related to surfaces. Add REPORT, VARIABLE
DICTIONARY; to the idf, run the file, and review the rdd output file, searching
for "Surface". For definitions of report variables, search the I/O Reference.
Also add DIAGNOSTICS, DisplayAdvancedReportVariables;
To report CTF coefficients, use REPORT, CONSTRUCTION;
This report may be found in the eio output file.
Regarding the last question, there is also radiant transfer to the sky and
ground.
Mike
On 15 Mar 2007 at 14:55, cienty1 wrote:
> Hello everyone, I am currently working on my master's project which
> involves the use of eplus. I have made a simple model of one wall to
> compare it with manual calculations but I have found I lack the
> following information.
>
> 1- Is there a variable that contains the external heat gain for a
> surface? or better yet is there a list of advance variables (like heat
> gains, CTF coefficients, etc.?
>
> 2- If I turn off wind and sun for the surface is there any other heat
> gain variable other than UAdeltaT(db)? (I am trying to do a simple
> UAdetaT model).
>
> Thanks.
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/