Re: [EnergyPlus_Support] Dual Fan + Single Duct VAV w/ perimeter reheat



The fans must be combined into a single fan for the simulation.

Yes, the VAVSingleDuctReheatBaseboard example file would be appropriate.  

Also see CompactHVAC-5ZoneVAVWaterCooled.idf.  This will show how to use 
Compact HVAC objects to set up the VAV portion of the system, and then you can 
take the expidf, rename it to NewFileName.idf and add the baseboard components. 
 This may save some time setting up the air loop.

Mike


On 13 Mar 2007 at 17:22, berlinclownfish wrote:

> Dear EnergyPlus support,
> 
> I'm trying to model an office building that has
> a) two supply and return fans installed in the AHU
> b) single duct VAV with hot water radiators on its perimeter.
> 
> For a), is it possible to model them separately (parallel) or do they 
> need to be combined? 
> 
> In regards, to b), what is the appropriate example from E+ example 
> files folder 'VAVSingleDuctReheatBaseboard'?
> 
> Any feedback is appreciated,
> 
> Sandro
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/