Re: [EnergyPlus_Support] Shading Surface Reflectance referencing Surface:Shading:Detached:Building?
In the BUILDING object, the Solar Distribution field must be set to
"FullExteriorWithReflections" or "FullInteriorAndExteriorWithReflections".
Mike
On 5 Jul 2007 at 10:24, ooikoonbeng2004 wrote:
> Hello everyone,
>
> If what i type for subject is wrong, please correct me.
>
> i entered the name "Wall of Virtual Lab" into the User Supplied
> Surface Name and 4 vertices into the Surface:Shading:Detached:Building
> object. i also entered "Wall of Virtual Lab" into the "Name of
> Surface: Shading object" field of the Shading Surface Reflectance
> object.
>
> i got the following warning:
>
> ** Warning ** The following lines are "Orphan Objects". These objects
> are in the idf
> ** ~~~ ** file but are never obtained by the simulation and
> therefore are NOT used.
> ** ~~~ ** See InputOutputReference document for more details.
> ************* Object=SHADING SURFACE REFLECTANCE=WALL OF VIRTUAL LAB
>
> Any help would be much appreciated, for i do have a wall near the
> building envelope that i think is reflecting solar radiation.
>
> Many thanks.
>
> ooi
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/