RE: [EnergyPlus_Support] Environmental Impact Factors & Fuel Factors
If what you say is true, then the TDV functionality described in the literature is not functional because the emissions will not change no matter what the scheduled values are.
Does this also that the emission factors as listed in the literature by state for electricity will not yield acceptable results unless they are multiplied by the source energy factor outside of energy plus?
"Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
My understanding is that all of the Fuel Factors are per unit of end-use
energy. There is no interaction between the various factors. I will make a
note to add some clarification to the documentation.
So, for electricity, a reduction in transmission losses would require a
proportional change to all of the fuel factors for electricity.
Mike
On 27 Aug 2007 at 6:32, Fortier Engineering wrote:
> I went back and double checked all my work and made the difference between the
> two runs was was even larger to make sure just running the similation for the
> two design days was enough to detect a difference in their emissions. There
> still is no difference betwee the output values.
>
> The three input objects for the low simulation are
>
> ENVIRONMENTAL IMPACT FACTORS,
> 0.3, !- Purchased Heating Efficiency
> 3.4, !- Purchased cooling COP
> 0.25, !- Steam Conversion Efficiency
> 80.7272, !- Total Carbon Equivalent Emission factor from NOx
> 6.2727, !- Total Carbon Equivalent Emission factor from CH4
> 0.2727; !- Total Carbon Equivalent Emission factor from CO2
>
> Fuel Factors,
> Electricity, !- Name of existing resource
> kg, !- Measure units (kg or m3)
> , !- J per measure unit factor
> 1, !- Source energy factor (J/J)
> Const Emissions, !- Source energy schedule FanAvailSched
> 159.26132, !- CO2 emission factor (g/MJ)
> , !- CO2 emission factor schedule
> 1.85885E3, !- CO emission factor (g/MJ)
> , !- CO emission factor schedule
> 1.34818E-3, !- CH4 emission factor (g/MJ)
> , !- CH4 emission factor schedule
> 3.29232E-1, !- NOx emission factor (g/MJ)
> , !- NOx emission factor schedule
> 2.55776E-3, !- N2O emission factor (g/MJ)
> , !- N2O emission factor schedule
> 1.25834, !- SO2 emission factor (g/MJ)
> , !- SO2 emission factor schedule
> 2.21604E-2, !- PM emission factor (g/MJ)
> , !- PM emission factor schedule
> 2.20060E-2, !- PM10 emission factor (g/MJ)
> , !- PM10 emission factor schedule
> 1.54356E-4, !- PM2.5 emission factor (g/MJ)
> , !- PM2.5 emission factor schedule
> 1.47657E-4, !- NH3 emission factor (g/MJ)
> , !- NH3 emission factor schedule
> 1.51542E-3, !- NMVOC emission factor (g/MJ)
> , !- NMVOC emission factor schedule
> 6.56449E-6, !- Hg emission factor (g/MJ)
> , !- Hg emission factor schedule
> 0, !- Pb emission factor (g/MJ)
> , !- Pb emission factor schedule
> 0, !- Water emission factor (L/MJ)
> , !- Water emission factor schedule
> 0, !- Nuclear High Level emission factor (g/MJ)
> , !- Nuclear High Level emission factor schedule
> 0, !- Nuclear Low Level emission factor (g/MJ)
> ; !- Nuclear Low Level emission factor schedule
> Fuel Factors,
> Natural Gas, !- Name of existing resource
> kg, !- Measure units (kg or m3)
> , !- J per measure unit factor
> 1, !- Source energy factor (J/J)
> Const Emissions, !- Source energy schedule
> 50.23439, !- CO2 emission factor (g/MJ)
> , !- CO2 emission factor schedule
> 3.51641E-2, !- CO emission factor (g/MJ)
> , !- CO emission factor schedule
> 9.62826E-4, !- CH4 emission factor (g/MJ)
> , !- CH4 emission factor schedule
> 4.1862E-2, !- NOx emission factor (g/MJ)
> , !- NOx emission factor schedule
> 9.20964E-4, !- N2O emission factor (g/MJ)
> , !- N2O emission factor schedule
> 2.51172E-4, !- SO2 emission factor (g/MJ)
> , !- SO2 emission factor schedule
> 3.18151E-3, !- PM emission factor (g/MJ)
> , !- PM emission factor schedule
> 2.38613E-3, !- PM10 emission factor (g/MJ)
> , !- PM10 emission factor schedule
> 7.95378E-4, !- PM2.5 emission factor (g/MJ)
> , !- PM2.5 emission factor schedule
> 0, !- NH3 emission factor (g/MJ)
> , !- NH3 emission factor schedule
> 2.30241E-3, !- NMVOC emission factor (g/MJ)
> , !- NMVOC emission factor schedule
> 1.08841E-7, !- Hg emission factor (g/MJ)
> , !- Hg emission factor schedule
> 2.09310E-7, !- Pb emission factor (g/MJ)
> , !- Pb emission factor schedule
> 2.1007, !- Water emission factor (L/MJ)
> , !- Water emission factor schedule
> 0, !- Nuclear High Level emission factor (g/MJ)
> , !- Nuclear High Level emission factor schedule
> 0, !- Nuclear Low Level emission factor (g/MJ)
> ; !- Nuclear Low Level emission factor schedule
> REPORT ENVIRONMENTAL IMPACT FACTORS,
> monthly; !- Reborting Frequency
>
> SCHEDULE:COMPACT,
> Const Emissions, !- Name
> Fraction, !- ScheduleType
> Through: 12/31,
> For: AllDays,
> Until: 24:00, 1.0;
>
> And for the high the only change is
>
> 100, !- Source energy factor (J/J)
>
> for the electricity fuel factor.
>
> Just to make sure it wasnt my file, I copy and pasted these three objects into
> the "CompactHVAC-5ZoneFanCoil.idf" to see if I could detect a difference and
> still was not able to detect one.
>
> I will be happy to upload my files if you would like to look them over.
>
> Thanks,
>
> Joe Lewis
> Fortier Engineering
>
>
> "Griffith, Brent" <brent_griffith@xxxxxxxx> wrote:
> Changing (lowering) the source energy factor in a Fuel Factors object
> is
> the right thing to do. It should be working. Check that you have all
> three objects in your input file: "Report Environmental Impact
> Factors", "Environmental Impact Factors" and "Fuel Factors"
>
> I think the source data that ships with EnergyPlus is EPA egrid data for
> 1999. There are newer emissions factors in this report:
>
> http://www.nrel.gov/docs/fy07osti/38617.pdf
>
> ________________________________
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of
> fortierengineering
> Sent: Friday, August 24, 2007 1:45 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Environmental Impact Factors & Fuel
> Factors
>
> I have modeled a building in Pennsylvania and to start I have used the
> electricity and natural gas fuel factors found in the data sets as well
> as the Environmental Impact Factors to determine the emissions
> contributions from this building.
>
> When I spoke with the local electricity company they advised me that
> the transmission losses for this location were lower than the state
> average. They did not have information reguarding the exact g/J of
> emission break down.
>
> I cannot figure out what field controls the electricity transmission
> losses.
>
> I thought it was the "J per measured unit factor" or the "source energy
> factor", but changing either of these fields does not affect any of the
> emission factors (ran the simulation at 1.827, then 1, then 10 and the
> emission totals turned out exactly the same).
>
> What are these two fields used for if they have no effect on the final
> data, and what is the best way to express a reduction in transmission
> losses?
>
> Thank you,
>
> Joseph Lewis
> Fortier Engineering
>
> [Non-text portions of this message have been removed]
>
>
>
>
>
>
> ---------------------------------
> Shape Yahoo! in your own image. Join our Network Research Panel today!
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
---------------------------------
Luggage? GPS? Comic books?
Check out fitting gifts for grads at Yahoo! Search.
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/