Re: [EnergyPlus_Support] Temperature and humidity setpoints
You can add an air-loop system to serve the same zones that are being served by
the radiant panels. By adding dehumdification controls, the air system can
control for humidity (cooling priority 1 in the zone equipment list) and the
radiant panels can pick up the remaining sensible load (cooling priority 2).
If you already have an air system described and want to add humidity controls,
see exmple file 5ZoneWaterCooled_HighRHControl.idf (chilled water system) or
FurnaceWithDXSystemRHcontrol.idf (DX system).
If you have not already set up the air system description, the quickest way to
would be to use COMPACT HVAC unitary or VAV objects. Get the updated COMPACT
HVAC interim release from the yahoo group files area
(CompactHVACInterimUpdateV2-0-0.zip in the Updates folder). This update
includes humidity control options on the VAV and unitary system types. If you
add this to your idf which already contains the radiant system, the run will
fail, because COMPACT HVAC will create duplicate instances of CONTROLLED ZONE
EQUIPMENT and ZONE EQUIPMENT LIST. Take the expidf output file and edit it to
merge these objects for the two systems.
Mike
On 14 Sep 2007 at 7:35, lorenzomattarolo wrote:
> Dear E+ support,
>
> I'm analysing an office building.
> The temperature of the office is controlled by a radiant system with
> panels on the ceiling.
> Besides an air system supplies primary air at a temperature of 16°C
> and at variable humidity. It varies the content of humidity according
> to a setpoint of 50% H.R. inside the office.
>
> I'm modelling this office with E+ by a system with radiant panels
> which control the temperature of the zone
> (by means of "zone control thermostatic" with "heating/cooling single
> setpoint")
>
> How can I model this air system?
> Is there a way to control the temperature of the zone by the radiant
> system and the humidity of the zone by an air system?
>
> Many thanks,
>
> Lorenzo
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/