[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Temperature and humidity setpoints
Dear Michael,
thanks a lot for your suggestions.
1. I'm trying to use the Compact:HVAC:system:VAV but I can't
understand what input I should add in the ID:A27 "humidifier type".
2. In order to have the setpoint of 50 HR into the zone all the time,
I'm using both humidifier and dehumification.
However I read that humidifier and dehumidification must use different
control zone.
How can I solve it?
Many thanks,
Lorenzo
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> You can add an air-loop system to serve the same zones that are
being served by
> the radiant panels. By adding dehumdification controls, the air
system can
> control for humidity (cooling priority 1 in the zone equipment list)
and the
> radiant panels can pick up the remaining sensible load (cooling
priority 2).
>
> If you already have an air system described and want to add humidity
controls,
> see exmple file 5ZoneWaterCooled_HighRHControl.idf (chilled water
system) or
> FurnaceWithDXSystemRHcontrol.idf (DX system).
>
> If you have not already set up the air system description, the
quickest way to
> would be to use COMPACT HVAC unitary or VAV objects. Get the
updated COMPACT
> HVAC interim release from the yahoo group files area
> (CompactHVACInterimUpdateV2-0-0.zip in the Updates folder). This
update
> includes humidity control options on the VAV and unitary system
types. If you
> add this to your idf which already contains the radiant system, the
run will
> fail, because COMPACT HVAC will create duplicate instances of
CONTROLLED ZONE
> EQUIPMENT and ZONE EQUIPMENT LIST. Take the expidf output file and
edit it to
> merge these objects for the two systems.
>
> Mike
>
>
> On 14 Sep 2007 at 7:35, lorenzomattarolo wrote:
>
> > Dear E+ support,
> >
> > I'm analysing an office building.
> > The temperature of the office is controlled by a radiant system with
> > panels on the ceiling.
> > Besides an air system supplies primary air at a temperature of 16°C
> > and at variable humidity. It varies the content of humidity according
> > to a setpoint of 50% H.R. inside the office.
> >
> > I'm modelling this office with E+ by a system with radiant panels
> > which control the temperature of the zone
> > (by means of "zone control thermostatic" with "heating/cooling single
> > setpoint")
> >
> > How can I model this air system?
> > Is there a way to control the temperature of the zone by the radiant
> > system and the humidity of the zone by an air system?
> >
> > Many thanks,
> >
> > Lorenzo
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@...
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/