Re: [EnergyPlus_Support] longwave radiation from the environment



1.  Yes.  See Engineering Reference discussion of convection algorithms, p. 42, 
pdf p. 78)

2.  I suspect that you have set the wind exposure to "NoWind" on the 
surface:heatransfer object.  See the discussion of this in the Input Output 
Reference, p. 139, pdf p. 178.  NoWind overrides the OUTSIDE CONVECTION option 
and forces it back to Simple.  Change this to WindExposed and the radiant 
coefficients should show non-zero values.

Mike


On 18 Sep 2007 at 13:44, friedl decock wrote:

> So the report variable ' Surface Ext *Convection* Coeff[W/m2-K](TimeStep)'
> for simple convection algorithm means the *total* exterior heat transfer
> coefficient (radiant and convective) and is independent from the surface
> emissivity.
> 
> I tried already all the other convection algorithms (detailed, TARP,
> DOE-2...), but I still get zero for the radiant heat coefficients. I also
> have the impression that the convective heat transfer coefficient stays the same
> as calculated with the simple convection algorithm. Do I need to set other
> settings beside the 'outside convection algorithm'?
> 
> Thank you for your help,
> Friedl
> 
> On 9/17/07, Michael J. Witte <mjwitte@xxxxxxxx> wrote:
> >
> >   The exterior radiant coefficients will be zero when OUTSIDE CONVECTION
> > is set
> > to "simple". The "simple" convection algorithms use a combined convection-
> > radiation coefficient and additional radiant transfer is not modeled.
> >
> > To see values in these variables, use the "Detailed" OUTSIDE CONVECTION
> > option.
> > These are the "simple" and "detailed" methods referred to in the TARP
> > manual,
> > however, the coefficients may be slightly different than what is found in the
> > TARP manual. The detailed convection model is based on ASHRAE equations.
> >
> > Mike
> >
> > On 17 Sep 2007 at 10:58, friedl decock wrote:
> >
> > > I'm trying to get the different heat fluxes through a wall out of a
> > > simulation.
> > > Everything seems to be fine for the interior surface heat balance. But I
> > > encounter some problems with the outside surface heat balance,
> > especially
> > > with the longwave radiation from the environment.
> > >
> > > 1. If I try to calculate qLWR with the formulas on p.36 (in the
> > engineering
> > > reference document) and with the output from a simulation (surface
> > temperatures,
> > > sky temperature, outside air temperature), there is a big difference
> > between the
> > > 'calculated qLWR' and the flux out of the simulation ( = [Surface Inside
> > Face
> > > Conduction] - [qSOL] - [qconv,exterior]). (There is no thermal storage
> > (density
> > > = specific heat = 0)).
> > >
> > > 2. If I'm asking for the report variables: Surface Ext Rad to Air Coeff,
> > > Surface Ext Rad to Sky Coeff, Surface Ext Rad to Ground Coeff, they are
> > > always zero. Do you need to do something special to get those report
> > > variables?
> > >
> > > 3. In the engineering reference document p.60 basic heat balance:
> > > "TARP includes four possible representations for the basic outside
> > surface
> > > heat balance. The first two depend on which of the optimal surface
> > > conductance algorithms the user selects. The simple outside surface
> > > conductance that includes both the convective and thermal interchange
> > > between the surface and the environment in a single coefficient, " ... "
> > The
> > > detailed outside surface conductance model considers convection and
> > radiation
> > > interchange with the sky and with the ground as seperate factors."
> > >
> > > 3a. How can you chose the optimal surface conductance algorithm?
> > > 3b. What's the value of the single coefficient? Does it take the
> > emissivity of
> > > the surface into account? 3c. The detailed outside surface conductance
> > seems to
> > > be almost the same as mentioned on p.35, accept that I don't see the
> > radiative
> > > heat transfer coeff to the air in figure 28 on p.62. (HA = outside
> > convection
> > > coefficient) (Or is HA a single value for radiation and convection?)
> >
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support
> > EnergyPlus-Support@xxxxxxxx <EnergyPlus-Support%40gard.com>
> >
> > 
> >
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/