Re: [EnergyPlus_Support] solar powered intermittent absorption refrigeration unit
Sorry, but this cannot be done with the current EnergyPlus absorption chiller.
The best I can suggest is to report hourly solar hot water gains and chilled
water loads and compute the results in a spreadsheet.
Mike
On 22 Nov 2007 at 13:03, Ashfaque Ahmed Chowdhury wrote:
> Dear all,
>
> I would like to model a solar powered intermittent absorption
> refrigeration unit to justify the feasibility of the unit on solar
> power.Is there any way so that I can connect the absorption
> refrigeration unit directly with the solar collectors in EP?
>
> Warmest regards,
> Ashfaque
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jun Calixihan"
> <jcalixihan@...> wrote:
> >
> > Hi!
> >
> >
> >
> > Need help identifying source of error in my model for absorption
> chiller.
> > Below is the error. I tried editing the condenser pump, chiller
> parameters,
> > equipment sizes, loop temperatures, etc. but can't seem to arrive
> at the
> > source of error. I uploaded the idf file named
> > AbsorptionChillerModified.idf
> >
> >
> >
> > Thank you in advance!
> >
> >
> >
> > Best Regards,
> >
> > Jun
> >
> >
> >
> >
> >
> > ** Warning ** SizeCondDemandSide: Calculated Plant Sizing Design
> Volume Flow
> > Rate=[0.00] is too small. Set to 0.0
> >
> > ** ~~~ ** ..occurs for Condenser Loop=CHILLED WATER LOOP
> CONDENSER
> > WATER LOOP
> >
> > ** Warning ** SizeCondSupplySide: Calculated Plant Sizing Design
> Volume
> > Flow Rate=[0.00] is too small. Set to 0.0
> >
> > ** ~~~ ** ..occurs for Condenser Loop=CHILLED WATER LOOP
> CONDENSER
> > WATER LOOP
> >
> > ** Warning ** SizePump: Calculated Pump Nominal Volume Flow Rate=
> [0.00]
> > is too small. Set to 0.0
> >
> > ** ~~~ ** ..occurs for Pump=CHILLED WATER LOOP CNDW SUPPLY
> PUMP
> >
> > ** Warning ** Check input. Pump nominal power or motor
> efficiency is set
> > to 0, for pump=CHILLED WATER LOOP CNDW SUPPLY PUMP
> >
> > ** Warning ** Check input. Pump nominal volumetric flow rate is
> set or
> > calculated = 0, for pump=CHILLED WATER LOOP CNDW SUPPLY PUMP
> >
> > ** Severe ** CalcBLASTAbsorberModel: Condenser flow = 0, for
> > Absorber=CHILLER
> >
> > ** Fatal ** Program Terminates due to previous error condition.
> >
> > ...Summary of Errors that led to program termination:
> >
> > ..... Reference severe error count=1
> >
> > ..... Last severe error=CalcBLASTAbsorberModel: Condenser flow =
> 0, for
> > Absorber=CHILLER
> >
> > ************* Fatal error -- final processing. More error
> messages may
> > appear.
> >
> > ************* Testing Individual Branch Integrity
> >
> > ************* All Branches passed integrity testing
> >
> > ************* Testing Individual Supply Air Path Integrity
> >
> > ************* All Supply Air Paths passed integrity testing
> >
> > ************* Testing Individual Return Air Path Integrity
> >
> > ************* All Return Air Paths passed integrity testing
> >
> > ************* No node connection errors were found.
> >
> > ************* EnergyPlus Terminated--Fatal Error Detected. 8
> Warning; 1
> > Severe Errors; Elapsed Time=00hr 00min 2.91sec
> >
> >
> >
> >
> >
> >
> >
> >
> >
> > [Non-text portions of this message have been removed]
> >
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/