Re: [EnergyPlus_Support] Re: Suspended radiant panels



Hey Michael;

The problem I'm having is that the "interzone surfaces are usually in a
different zone" message doesn't come in the context of a warning, but that
of an error. Specifically:

   ** Severe  ** CAUTION -- Interzone surfaces are usually in different
zones
   **   ~~~   ** Surface=OBJ:0025, Zone=ZONE_1
   **   ~~~   ** Surface=OBJ:0026, Zone=ZONE_1

When I model the system like this, the simulation won't run. Do interzone
surfaces being in the same zone *usually* crash the simulation?

Thanks,

Josh


On Dec 6, 2007 11:59 AM, Michael J. Witte <mjwitte@xxxxxxxx> wrote:

>   Using the adiabatic approach will not result in radiant transfer from
> the top
> side of the radiant panel to the ceiling of the zone. Adiabatic surfaces
> simply model the inside face heat balance and then set the opposite side
> temperature to the same value. The other side of the surface is not
> modeled
> and is not present in any zone.
>
> You need to go with the pair of interzone surfaces. In doing so, you can
> ignore "interzone durfaces are usually in different zone" warning. It's
> just
> there to warn that what you've described might be a mistake (an easy
> mistake to
> make if you copy the first surface to create the opposite surface and
> forget to
> change the zone name if you really intend this to sit between two zones).
> This
> configuration will simulate both sides as active surfaces in the zone.
>
> Mike
>
>
> On 5 Dec 2007 at 19:51, josh_miarch wrote:
>
> > Hi Mike;
> >
> > I'm also doing a simulation with a suspended radiant panel, and I've
> > found that if I define another opposite-facing surface and connect it
> > as an "interzone" surface with the radiant surface, I either get a
> > bunch of "heat balance did not converge" warning messages, or an
> > "Interzone surfaces are usually in different zones" error message,
> > depending on how I specify the constructions of the hydronic surface
> > and its backing.
> >
> > However, if I specify the radiant surface as one would an adiabatic
> > surface (ie OtherZoneSurface = itself), I seem to get reasonable
> results.
> >
> > Any thoughts on this?
> >
> > Thanks,
> >
> > Josh
> >
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx<EnergyPlus_Support%40yahoogroups.com>,
> "Michael J. Witte"
> > <mjwitte@...> wrote:
> > >
> > > 1. I suppose you could describe a surface which is positioned as
> > thought it is
> > > supsended. This would have to be a pair of surfaces (one facing up
> > and one
> > > facing down) which are connected as "interzone" surfaces even though
> > both are
> > > in the same zone. But understand that the radiant view factor
> > calculations are
> > > not full 3-D. View factors are affected by azimuths and tilts, but
> > position in
> > > the zone does not matter. If the radiant panels are electric, you
> > could use
> > > the high temperature radiant model (HIGH TEMP RADIANT SYSTEM) and
> > specify the
> > > view factors directly.
> > >
> > > 2. Low temp radiant systems are only valid on base surfaces (not
> > subsurfaces,
> > > no internal mass). You would need to describe the ceiling as two or
> > more
> > > SURFACE:HEATRANSFER objects, one with the area of the radiant panel,
> > and one
> > > with the remaining ceiling area.
> > >
> > > Mike
> > >
> > >
> > > On 5 Sep 2007 at 13:21, lorenzomattarolo wrote:
> > >
> > > > Hi,
> > > > I'm simulating an office with radiant panels on the ceiling.
> > > >
> > > > 1. Is it possible to put the radiant panels as they were suspended
> > > > from the ceiling?
> > > >
> > > > 2. The panels aren't as wide as the ceiling. How can I set this in
> the
> > > > surfaceHeatTransfer? Do I have to put one surface with a normal
> > > > construction for the ceiling and a smaller one with internal source
> > > > for the panel?
> > > >
> > > > Many thanks,
> > > >
> > > > Lorenzo
> > > >
> > > >
> > > >
> > > > The primary EnergyPlus web site is found at:
> > > > http://www.energyplus.gov
> > > >
> > > > The group web site is:
> > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > >
> > > > Attachments are not allowed -- please post any files to the
> > appropriate folder
> > > > in the Files area of the Support Web Site.
> > > >
> > > > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
> > under the
> > > > Documentation link and press the "search" button.
> > > >
> > > > Yahoo! Groups Links
> > > >
> > > >
> > > >
> > > >
> > > >
> > >
> > >
> > > ========================================================
> > > Michael J. Witte, GARD Analytics, Inc.
> > > EnergyPlus Testing and Support
> > > EnergyPlus-Support@...
> > >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate
> folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> > Documentation link and press the "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx <EnergyPlus-Support%40gard.com>
>
>  
>



-- 
Josh Kjenner, EIT, LEED AP
Manasc Isaac Architects Ltd.
10225 100 Avenue :: Edmonton, AB T5J 0A1
780.429.3977


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/