Re: [EnergyPlus_Support] A question about primary and secondary loop configuration
Thanks, Mike.
I have two further questions.
1. The compact HVAC chilled water loop does not allow variable flow for both primary and decondary, it only allows varible+constant or constant+variable.
2. When I create two separate chilled water loops. I will create two chillers. How can I create two chilled water loops with only one chiller?
Thanks a lot for your help.
Regards,
Zhen
"Michael J. Witte" <mjwitte@xxxxxxxx> wrote: If you want to create two separate chilled water loops using COMPACT HVAC, you
must make two different idf files, and then merge them expidf files by hand
using a text editor.
For this particular application, it may work for you to use COMPACT HVAC to
create a chilled water loop serving the cooling coils with variable flow
primary and variable flow secondary. Then, using the expidf file, add LOW TEMP
RADIANT SYSTEM:CONSTANT FLOW to the simulation.
Mike
On 20 Dec 2007 at 11:02, Zhen Tian wrote:
> Dear all,
>
> I have a question about the configuration of primary and secondary chilled water
> loops.
>
> The primary chilled water loop has variable flow pump. Connected secondary loops
> have two pumps, one constant flow pump for radiant panels and one variable flow
> pump for cooling coils. In the compact HVAC, it does not allow two chilled water
> loops. Does anyone has experience how to arrange this configuration?
>
> Thanks a lot in advance.
>
> Regards,
>
> David
>
>
> ---------------------------------
> Looking for last minute shopping deals? Find them fast with Yahoo! Search.
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
---------------------------------
Be a better friend, newshound, and know-it-all with Yahoo! Mobile. Try it now.
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/