RE: [EnergyPlus_Support] Re: U value input
I don't quite follow you, I ran your files and they seem to be reporting
similarly. If you are looking at the Envelope Summary in the html
report, there does seem to be a problem with reporting of "U Factor with
Film".
But in general, the best approach is to use the E+ report for U-values
without the film coefficients and then apply the film coefficients
yourself so that they agree with what the Standard is expecting.
Internally E+ doesn't use crude combined convection/radiation film
coefficients so reporting with the film coefficients is somewhat
arbitrary. E+ is neutral with respect to specific Standards and it may
be that there are different film coefficients that need to be used
depending on the Standard.
It is important to understand that film coefficients, and hence U-values
with film coefficients, depend on orientation (vertical, horizontal heat
flow up, horizontal heat flow down, etc) and are not uniquely defined
for just constructions. So the reporting of these is by surface, not by
construction. To get a report in eio file with film coefficients you
would need to add a "Report, surfaces, details;" input object to the idf
file. See page 23 (or 29 absolute) in OutputDetailsAndExamples.pdf for
more information.
________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of eric_zhou1223
Sent: Tuesday, January 22, 2008 10:55 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Re: U value input
Thanks a lot, Brent. I used the tool to output two files, the only
difference between them being location and perhaps system type. Yet
one of them can report "U-Factor with Film " and "U-Factor no Film",
another can only report "U-Factor no Film". Would you please give
me hint on this? Thanks again. I uploaded two files package named "U
factor".
Eric
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx
<mailto:EnergyPlus_Support%40yahoogroups.com> , "Griffith, Brent"
<brent_griffith@...> wrote:
>
> Not directly. E+ uses layer-by-layer descriptions and targeting a
> specific U-value often requires iteration. Tune the material
properties
> of an insulation layer inside the construction. Be careful about
the
> surface film coefficients when setting targets... (E+ can report
them
> with or without, but Standards aren't always so clear). If the
Standard
> is 90.1, you could try constructions out of an input file from the
> EnergyPlus Example File Generator.
>
>
>
> ________________________________
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
<mailto:EnergyPlus_Support%40yahoogroups.com>
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx
<mailto:EnergyPlus_Support%40yahoogroups.com> ] On Behalf Of
eric_zhou1223
> Sent: Thursday, January 17, 2008 12:27 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
<mailto:EnergyPlus_Support%40yahoogroups.com>
> Subject: [EnergyPlus_Support] U value input
>
>
>
> Hi all,
>
> Is there a simple way to define an U value for a wall,which is
made of
> several layers, like in eQuest? Given that I need to set the wall
U-
> value to a standard value.
>
> Eric
>
>
>
>
>
> [Non-text portions of this message have been removed]
>
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/