RE: [EnergyPlus_Support] Design Builder vs Energy Plus - Maximum U-Value
Josep's approach is good.
If you prefer to use your approach, I do not think there is a hard limit, but
you will probably find that the convection coefficients for the "bridge"
surfaces must be increased or they will become the primary resistance of these
surfaces. Use the ConvectionCoefficients object to set these.
Mike
On 20 Feb 2008 at 9:28, josep.sole@xxxxxxxxxxx wrote:
> In order to introduce the thermal bridges impact I usually use a "small"
> sub-surface in aproximatively at the same position than in the building.
>
>
>
> For the thermal bridging construction I use a very simple; only one layer
> defined by it's R value pre calculated in manner that the thermal transmittance
> resultant is the same considering this construction and it's surface than the
> linear thermal transmittance and it's length.
>
>
>
> I didn't found any problems to calculate in this way due to U (or R) value.
>
>
>
> In my opinion it's not possible to do this approach on DesignBuilder but yes on
> Energy+
>
>
>
>
>
> Josep Solé
> URSA Ibérica Aislantes SA - URALITA
> Dirección Técnica
> C/ caspe nº 17 6ªPlanta
> 08010 - Bareclona - España
> Tel +34 344 11 00
> Tel IP +34 93 344 11 36
> Móvil +34 606 42 32 14
> Fax +34 344 11 00
>
> www.ursa.es <http://www.ursa.es/>
>
> www.ursa-online.com <http://www.ursa-online.com/>
>
> www.uralita.com <http://www.uralita.com/>
>
>
>
>
> P URALITA / URSA se compromete con el ahorro de energía. Antes de imprimir este
> mensaje asegúrese de que es necesario.
>
> ________________________________
>
> Aviso de confidencialidad
> Este mensaje contiene información que puede ser confidencial y de uso
> restringido. Si usted no es el receptor deseado del mensaje (ni está autorizado
> a recibirlo por éste) no está autorizado a copiar, reenviar, o por otra parte,
> divulgar el mensaje o su contenido a cualquier otro. Si ha recibido este mensaje
> por error, por favor, notifíquenoslo inmediatamente y bórrelo de su sistema.
>
> ________________________________
>
> De: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] En nombre de André Lopes Enviado el:
> martes, 19 de febrero de 2008 20:08 Para: EnergyPlus Support Asunto:
> [EnergyPlus_Support] Design Builder vs Energy Plus - Maximum U-Value
>
>
>
> Hi
>
> What can be the maximum U-Value that the Design Builder or the Energy Plus can
> calculate? See the attacched picture.
>
> The objective is to put in 1 square meter per Zone the losses due to the Thermal
> Bridges (Linear and Superficial), so in this case the U-value can be 200 or 300
> W/m2.ºK
>
> Regards
>
> A L
>
> __________________________________________________________
> Be a better friend, newshound, and
> know-it-all with Yahoo! Mobile. Try it now.
> http://mobile.yahoo.com/;_ylt=Ahu06i62sR8HDtDypao8Wcj9tAcJ
> <http://mobile.yahoo.com/;_ylt=Ahu06i62sR8HDtDypao8Wcj9tAcJ>
>
> [Non-text portions of this message have been removed]
>
>
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/