[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
RE: [EnergyPlus_Support] Error adding zone baseboard
You might have created the baseboard branch itself, but I think you don't have your baseboard heater on your Hot Water Loop Demand Side Branch List. Check this in your IDF file.
Matthew Flannery, LEED A.P.
Mechanical Engineer
Buro Happold Consulting Engineers, PC
100 Broadway
New York, NY 10005
USA
___
_____________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Alan Jackson
Sent: Thursday, May 01, 2008 2:47 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Error adding zone baseboard
I have added baseboard to a zone which already has vav reheat and
followed the methodology outlined in the example file
VAVSingleDuctReheatBaseboard for connecting the baseboard to the
demand side of the HW Loop and adding the proper branch but i am
getting the following error. Any advice would be appreciated. Thanks.
-
aj
************* Beginning System Sizing Calculations
************* Beginning Plant Sizing Calculations
** Severe ** Splitter Output Branch not found, Splitter=HOT WATER
LOOP HW DEMAND SPLITTER
** ~~~ ** Splitter Branch Outlet node name=LEVEL 6 ZONE 2
BASEBOARD INLET
** ~~~ ** In Loop=HOT WATER LOOP HOT WATER LOOP
** Severe ** Mixer Inlet Branch not found, Mixer=HOT WATER LOOP HW
DEMAND MIXER
** ~~~ ** Mixer Branch Inlet name=LEVEL 6 ZONE 2 BASEBOARD OUTLET
** ~~~ ** In Loop=HOT WATER LOOP HOT WATER LOOP
** Fatal ** GetPlantSideInput: Previous Severe errors cause termination.
....Summary of Errors that led to program termination:
...... Reference severe error count=2
...... Last severe error=Mixer Inlet Branch not found, Mixer=HOT WATER
LOOP HW DEMAND MIXER
************* Fatal error -- final processing. More error messages
may appear.
************* Testing Individual Branch Integrity
** Warning ** There are orphaned Branches in input
************* All Branches passed integrity testing
************* Testing Individual Supply Air Path Integrity
************* All Supply Air Paths passed integrity testing
************* Testing Individual Return Air Path Integrity
************* All Return Air Paths passed integrity testing
This message has been scanned by MailController.
Click here to report this email as spam.
This message has been scanned by MailController - www.MailController.altohiway.com
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/