Re: [EnergyPlus_Support] using two chillers in one system?
Are you autosizing your chillers? If so, each will be sized to meet the
entire load and reducing the capacity and water flow rate by a factor of
2 for each chiller may help. Look to the eio file for sizing results
when autosizing equipment.
lichunying83 wrote:
>
> I have used two chillers in my model. However, I find one of them is
> seldom used through the year. It only runs for an hour in the morning,
> when the whole HVAC system starts to run in summer.
>
> My goal is to let the two chillers both run in summer and one of them
> run in winter. But the summer condition is not satisfactory.
>
> I know this might be caused by the large cooling load in the morning
> when indoor air temperature is high and quick cooling is needed. I even
> changed the cooling temperature schedule to decrease this cooling load,
> but the affection is not good. Have anyone fix this before? How?
>
> Thank you!
>
> By the way, I run the example file of ElectricChiller.idf , the result
> is similar. The little chiller will not run through the whole year.
>
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/