[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Earth tubes and airflownetwork



Thank you, Lixing!  This is good to know. --Kristin

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Lixing Gu <gu@...> wrote:
>
> Kristin:
> 
> Both Earthtube and AirflowNetwork models can not work together right
now. 
> Here are answers to your testing:
> 
> 1     No airflownetwork objects
> 
> As mentioned early, both model can not work together. If both objects 
> co-exist, the AirflowNetwork mode supersedes the earthtube mode at two 
> control choices. Since the earthtube objects are not used, the "orphan" 
> warning is shown up.
> 
> 2    Warning occur
> 
> There are four control choices in the second field of the
AirflowNetwork 
> Simulation object:
> 
> MULTIZONE WITH DISTRIBUTION
> MULTIZONE WITHOUT DISTRIBUTION
> MULTIZONE WITH DISTRIBUTION ONLY DURING FAN OPERATION
> NO MULTIZONE OR DISTRIBUTION
> 
> When the first two choices are selected, the AirflowNetwork model
takes over 
> airflow calculation. The earthtube objects are not used in the airflow 
> calculation. The example file of
AirflowNetwork_Multizone_SmallOffice.idf 
> has the first choice. That is why the "orphan" warning occurs.
> 
> 3    not give me orphan warnings
> 
> The example file of AirflowNetwork_Simple_House.idf uses the third
choice. 
> The AirflowNetwork model is only used during HVAC operation time.
During 
> system off time, the earthtube model is used to calculate airflows.
That is 
> why no warning is given.
> 
> Thanks.
> 
> Lixing
> 
> ----- Original Message ----- 
> From: "Kristin Field" <fieldkm@...>
> To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
> Sent: Tuesday, July 22, 2008 11:07 PM
> Subject: [EnergyPlus_Support] Re: Earth tubes and airflownetwork
> 
> 
> > Thanks, Edwin.  Thinking about your example, I tried 3 things, and
> > here's what happened:
> >
> > 1. I took the file I had been working with (created by someone else,
> > but I couldn't readily see anything severely wrong with it) and
> > deleted the whole airflownetwork.  The warning that the earth tube
> > object was an "orphan" went away.
> >
> > 2. Since the above mentioned file used a multizone afn, I added one
> > earth tube to the AirflowNetwork_Multizone_SmallOffice.idf file.  It
> > gave me an orphan message similar to what the other file (from #1) had
> > been giving me:
> >
> >   ** Warning ** The following lines are "Orphan Objects".  These
> > objects are in the idf
> >   **   ~~~   **  file but are never obtained by the simulation and
> > therefore are NOT used.
> >   **   ~~~   **  See InputOutputReference document for more details.
> >   ************* Object=EARTHTUBE=RESISTIVE ZONE
> >
> > 3. As I think you did, I added an earth tube in the LIVING ZONE of the
> > AirflowNetwork_SimpleHouse.idf file.  This did not give me orphan
> > warnings.
> >
> > So it would seem to me that a certain level of complexity in the afn
> > makes it impossible for the earth tube model to run.  Would anyone
> > like to confirm or deny this?
> >
> > Thanks,
> > Kristin
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Edwin Lee" <leeed2001@>
> > wrote:
> >>
> >> Kristin:
> >>
> >> I didn't look into the full simulation results, but just for kicks,
> > I took
> >> the E+ example file AirflowNetwork_SimpleHouse, and added an earth
> > tube to
> >> the Living Zone.  E+ ran fully without any errors or warnings.
> >>
> >> Again, the results may be funny, but I would think if anything
had gone
> >> wrong, E+ would have complained.  The earth tube is set up simply as
> > zone
> >> equipment.  The earth tube will not directly interact with the
airflow
> >> network, but they will both be accounted for in the zone heat balance
> >> calculations.
> >>
> >> Edwin
> >>
> >> On Tue, Jul 22, 2008 at 1:13 PM, Kristin Field <fieldkm@> wrote:
> >>
> >> >   Clarification: could they both be used on the same zone if
one was
> >> > scheduled to operate during the summer and the other during the
winter
> >> > (i.e., same zone, but not same time)? I have a feeling the
answer is
> >> > no, but I thought I should check here just in case.
> >> >
> >> > --- In
> >
EnergyPlus_Support@xxxxxxxxxxxxxxx<EnergyPlus_Support%40yahoogroups.com>,
> >> > "Kristin Field"
> >> >
> >> > <fieldkm@> wrote:
> >> > >
> >> > > It seems to me from the way that the earth tube model is set
up that
> >> > > it is probably not possible to use earth tubes and the
> > airflownetwork
> >> > > on the same zone. Am I correct about that? If it is possible
to do
> >> > > both, does anyone have any guidance as to how?
> >> > >
> >> > > Thanks,
> >> > > Kristin
> >> > >
> >> >
> >> >
> >> >
> >>
> >
> >
> >
> > ------------------------------------
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate 
> > folder in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf
under the 
> > Documentation link and press the "search" button.
> > Yahoo! Groups Links
> >
> >
> >
> >
>



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/