Re: [EnergyPlus_Support] Heating/Cooling controlled setpoints



Do you have Daylight Saving period on in the summer?

It flexes the schedule time on/off

Linda


At 12:00 PM 8/1/2008, Richard Raustad wrote:
I am a little confused myself but if you look at the schedule values for
HTG/COOL  AVAILABILITY:Schedule Value you will see that the value goes
to 0 just after 18:00 in winter and just after 17:00 in summer. This is
why the Purchased Air system is turning off. Why this is happening will
need more time to figure out. You could try using a different schedule
name for the cooling availability schedule to see if you can get the
cooling to turn on from 7:00 to 18:00.

PURCHASED AIR,
    SALA PRINCIPAL Purchased Air,  !- Purchased Air Name
    SALA PRINCIPAL Supply Inlet,  !- Zone Supply Air Node Name
    50,                      !- Heating Supply Air Temp {C}
    13,                      !- Cooling Supply Air Temp {C}
    0.008,                   !- Heating Supply Air Humidity Ratio
{kg-H2O/kg-air}
    0.009,                   !- Cooling Supply Air Humidity Ratio
{kg-H2O/kg-air}
    NO LIMIT,                !- heating limit
    ,                        !- Maximum heating air flow rate {m3/s}
    NO LIMIT,                !- cooling limit
    ,                        !- Maximum cooling air flow rate {m3/s}
    NO OUTSIDE AIR,          !- outside air
    ,                        !- Outside air flow rate {m3/s}
    HTG/COOL  AVAILABILITY,  !- heating availability schedule
    HTG/COOL  AVAILABILITY;  !- cooling availability schedule

PURCHASED AIR,
    SALA SECUNDARIA Purchased Air,  !- Purchased Air Name
    SALA SECUNDARIA Supply Inlet,  !- Zone Supply Air Node Name
    50,                      !- Heating Supply Air Temp {C}
    13,                      !- Cooling Supply Air Temp {C}
    0.008,                   !- Heating Supply Air Humidity Ratio
{kg-H2O/kg-air}
    0.009,                   !- Cooling Supply Air Humidity Ratio
{kg-H2O/kg-air}
    NO LIMIT,                !- heating limit
    ,                        !- Maximum heating air flow rate {m3/s}
    NO LIMIT,                !- cooling limit
    ,                        !- Maximum cooling air flow rate {m3/s}
    NO OUTSIDE AIR,          !- outside air
    ,                        !- Outside air flow rate {m3/s}
    HTG/COOL  AVAILABILITY,  !- heating availability schedule
    HTG/COOL  AVAILABILITY;  !- cooling availability schedule

SCHEDULE:COMPACT,
    HTG/COOL  AVAILABILITY,  !- Name
    Any Number,              !- ScheduleType
    Through: 12/31,          !- Complex Field #1
    For: AllDays,            !- Complex Field #2
    Until: 7:00,             !- Complex Field #3
    0,                       !- Complex Field #4
    Until:18:00,             !- Complex Field #5
    1,                       !- Complex Field #6
    Until:24:00,             !- Complex Field #7
    0;                       !- Complex Field #8

.

Nuno Costa Brandão wrote:
>
> Dear All,
>
> I´m simulating a small building building museum in order to evaluate
> it´s rehabilitation. The building has two zones with heat/cool
> setpoint control (20-25ºC).
>
> The results show that in the Winter the control is effectively
> guarantee within the pretended period (8:00-18:00), but when analysing
> Summer the control defined with a heat/cool availability schedule, is
> only guaranteed from 8:00 to 17:00 although both Winter and Summer are
> affected with the same schedule. I have verified the schedules and
> they are perfectly defined. Can you please take a look to my idf file
> to give some guidance help?
>
> Thanks,
> Nuno
>
> 

--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/
__._,_.___

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___