Re: [EnergyPlus_Support] about stand-alone energy recovery ventilator
Check the controller object, the name can not be blank. Also make sure
there is only 1 comma on the first line.
CONTROLLER:STAND ALONE ERV, << only 1 comma here
>> ERV OA Controller 1, !- ERV controller name
llyymmff wrote:
>
> Hello, all
> I have a problem about simulation of stand-alone energy recovery
> ventilator (ERV). I want to use ERV in the heat pump: air to air
> system. I don't know if this is feasible. I add the ERV system into
> heat pump system according to the example file:
> HVACStandAloneERV_Economizer (this example is in a Window AC system).
> I always get the error warning just like the following:
> ** Severe ** CONTROLLER:STAND ALONE ERV Name, cannot be blank.
> I checked the IDF again and again, and I can be sure that I did input
> the CONTROLLER:STAND ALONE ERV Name. I cannot understand this, and
> could you please help me?
> Thank you very much!
> Best Regards!
>
> ym
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/