There's the answer, that unit has a variable compressor (let me know if
I am wrong, I only looked at the first web page). VRV systems modulate
the compressor speed, no real need to worry about the air flow volume
ratio. The system maintains a constant suction temperature and therefore
can not freeze the coil. E+ can not yet simulate a VRV (VRF) AC system.
Your only option for now is to raise the air flow per ton as you have
suggested. Take a close look at your results when you are finally able
to perform the simulation. I am interested to know how close you got to
simulating VRV AC system performance.
Adriano Carotenuto wrote:
>
> Dear Richard,
>
> It´s Daikin Manufacturer indoor unit model FXFQ125MVE (ceiling mounted
> cassete type - multi-flow)
> Specifications:
> Cooling capacity: 14000 W
> Air flow rate: 30 m3/min;
> I am trying to simulate the thermal zone with four indoor units (56000
> W) and maximum air flow rate (120 m3/min).
>
> The manual is Engineering Data, Nr ED 39-428B.
>
> The manual on the web site link is different from what I am using.
> http://www.daikinac.com/commercial/docsEngineering.asp?sec=docs&page=58
> <http://www.daikinac.com/commercial/docsEngineering.asp?sec=docs&page=58>
>
> I will send you the page with the data above.
>
> Thank you,
>
> Adriano Carotenuto.
>
>
> ----- Original Message -----
> *From:* Richard Raustad <mailto:RRaustad@xxxxxxxxxxxx>
> *To:* EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>
> *Sent:* Wednesday, December 03, 2008 3:45 PM
> *Subject:* Re: [EnergyPlus_Support] Rated air volume flow rate per
> watt of rated totalcooling capacity out of range
>
> Would you also please provide the manufacturer name and web site
> link so
> the E+ team can look at this data? Thank you.
>
> Edwin Lee wrote:
> >
> >
> > Does the simulation continue to run fine? Even though this is a
> > severe error, I don't think it will cause the simulation to
> cease, it
> > is just letting you know that this was encountered during the
> sizing
> > runs as it moves ahead with the simulation.
> >
> > Edwin
> >
> > On Wed, Dec 3, 2008 at 11:33 AM, Adriano Carotenuto
> > <adriano.carotenuto@xxxxxxxxxxxx
> <mailto:adriano.carotenuto%40terra.com.br>
> > <mailto:adriano.carotenuto@xxxxxxxxxxxx
> <mailto:adriano.carotenuto%40terra.com.br>>> wrote:
> >
> > Dear All,
> >
> > I am trying to simulate a thermal zone with Compact HVAC: Zone:
> > PTHP by entering the data from the manufacturer catalogue: 56000 W
> > rated total cooling capacity (gross) and 2,0 m3/s rated air
> > volume flow rate.
> > But, when I run the simulation, comes up a severe error as listed
> > below and the program stops running.
> >
> > Severe ** Sizing: COIL:DX:COOLINGBYPASSFACTOREMPIRICAL
> > "2O_PAV._ZONA1 PTHP COOLING COIL": Rated air volume flow rate per
> > watt of rated total cooling capacity is out of range. See
> > Input-Output Reference Manual for valid range.
> >
> > According to manual, the range is between 0,00004027 and 0,0006041
> > m3/s/W.
> >
> > The value of the manufacturer catalogue is 0,00003571 m3/s/W,
> > below the Energyplus range.
> >
> > Is there some way to "bypass" this error or to modify these limits
> > in the program?
> >
> > Please, I would appreciate if someone could help me in this
> question.
> >
> > Thank you.
> >
> > Adriano
> >
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> <http://www.fsec.ucf.edu>
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
> ------------------------------------------------------------------------
> E-mail verificado pelo Terra Anti-Spam.
> Para classificar esta mensagem como spam ou não spam, clique aqui
> <http://mail.terra.com.br/cgi-bin/reportspam.cgi?+_d=SCY5NzM1NDIwI3Blcm0hdGVycmEmMSwxMjI4MzI2NDUzLjcyNTE5LjE1NDI3LmNvc21vbGVkby5oc3QudGVycmEuY29tLmJyLDIwNDk3>.
> Verifique periodicamente a pasta Spam para garantir que apenas
> mensagens
> indesejadas sejam classificadas como Spam.
>
> ------------------------------------------------------------------------
> Esta mensagem foi verificada pelo E-mail Protegido Terra
> <http://mail.terra.com.br/>.
> Atualizado em 03/12/2008
>
> ------------------------------------------------------------------------
>
> No virus found in this incoming message.
> Checked by AVG - http://www.avg.com
> Version: 8.0.175 / Virus Database: 270.9.12/1824 - Release Date:
> 2/12/2008 09:31
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/