There's the answer, that unit has a variable compressor (let me know if
I am wrong, I only looked at the first web page). VRV systems modulate
the compressor speed, no real need to worry about the air flow volume
ratio. The system maintains a constant suction temperature and therefore
can not freeze the coil. E+ can not yet simulate a VRV (VRF) AC
system.
Your only option for now is to raise the air flow per ton as
you have
suggested. Take a close look at your results when you are finally
able
to perform the simulation. I am interested to know how close you got
to
simulating VRV AC system performance.
Adriano Carotenuto
wrote:
>
> Dear Richard,
>
> It´s Daikin Manufacturer
indoor unit model FXFQ125MVE (ceiling mounted
> cassete type -
multi-flow)
> Specifications:
> Cooling capacity: 14000 W
>
Air flow rate: 30 m3/min;
> I am trying to simulate the thermal zone
with four indoor units (56000
> W) and maximum air flow rate (120
m3/min).
>
> The manual is Engineering Data, Nr ED
39-428B.
>
> The manual on the web site link is different from
what I am using.
> http://www.daikinac.com/commercial/docsEngineering.asp?sec=docs&page=58
> <http://www.daikinac.com/commercial/docsEngineering.asp?sec=docs&page=58>
>
> I will send you the page with the data above.
>
> Thank
you,
>
> Adriano Carotenuto.
>
>
> -----
Original Message -----
> *From:* Richard Raustad <mailto:RRaustad@FSEC.UCF.EDU>
>
*To:* EnergyPlus_Support@yahoogroups.com
>
<mailto:EnergyPlus_Support@yahoogroups.com>
>
*Sent:* Wednesday, December 03, 2008 3:45 PM
> *Subject:* Re:
[EnergyPlus_Support] Rated air volume flow rate per
> watt of rated
totalcooling capacity out of range
>
> Would you also please
provide the manufacturer name and web site
> link so
> the E+ team
can look at this data? Thank you.
>
> Edwin Lee wrote:
>
>
> >
> > Does the simulation continue to run fine? Even
though this is a
> > severe error, I don't think it will cause the
simulation to
> cease, it
> > is just letting you know that
this was encountered during the
> sizing
> > runs as it moves
ahead with the simulation.
> >
> > Edwin
>
>
> > On Wed, Dec 3, 2008 at 11:33 AM, Adriano Carotenuto
>
> <adriano.carotenuto@terra.com.br
>
<mailto:adriano.carotenuto%40terra.com.br>
> >
<mailto:adriano.carotenuto@terra.com.br
>
<mailto:adriano.carotenuto%40terra.com.br>>>
wrote:
> >
> > Dear All,
> >
> > I am
trying to simulate a thermal zone with Compact HVAC: Zone:
> > PTHP
by entering the data from the manufacturer catalogue: 56000 W
> >
rated total cooling capacity (gross) and 2,0 m3/s rated air
> >
volume flow rate.
> > But, when I run the simulation, comes up a
severe error as listed
> > below and the program stops
running.
> >
> > Severe ** Sizing:
COIL:DX:COOLINGBYPASSFACTOREMPIRICAL
> > "2O_PAV._ZONA1
PTHP COOLING COIL": Rated air volume flow rate per
> > watt of rated
total cooling capacity is out of range. See
> > Input-Output
Reference Manual for valid range.
> >
> > According to
manual, the range is between 0,00004027 and 0,0006041
> >
m3/s/W.
> >
> > The value of the manufacturer catalogue is
0,00003571 m3/s/W,
> > below the Energyplus range.
>
>
> > Is there some way to "bypass" this error or to modify these
limits
> > in the program?
> >
> > Please, I would
appreciate if someone could help me in this
> question.
>
>
> > Thank you.
> >
> > Adriano
>
>
> >
> >
>
> --
> Richard A.
Raustad
> Senior Research Engineer
> Florida Solar Energy
Center
> University of Central Florida
> 1679 Clearlake
Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax:
(321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> <http://www.fsec.ucf.edu>
>
>
UCF - From Promise to Prominence: Celebrating 40 Years
>
>
----------------------------------------------------------
>
E-mail verificado pelo Terra Anti-Spam.
> Para classificar esta mensagem
como spam ou não spam, clique aqui
> <http://mail.terra.com.br/cgi-bin/reportspam.cgi?+_d=SCY5NzM1NDIwI3Blcm0hdGVycmEmMSwxMjI4MzI2NDUzLjcyNTE5LjE1NDI3LmNvc21vbGVkby5oc3QudGVycmEuY29tLmJyLDIwNDk3>.
>
Verifique periodicamente a pasta Spam para garantir que apenas
>
mensagens
> indesejadas sejam classificadas como Spam.
>
>
----------------------------------------------------------
>
Esta mensagem foi verificada pelo E-mail Protegido Terra
> <http://mail.terra.com.br/>.
>
Atualizado em 03/12/2008
>
>
----------------------------------------------------------
>
>
No virus found in this incoming message.
> Checked by AVG - http://www.avg.com
> Version: 8.0.175
/ Virus Database: 270.9.12/1824 - Release Date:
> 2/12/2008
09:31
>
>
--
Richard A. Raustad
Senior Research
Engineer
Florida Solar Energy Center
University of Central
Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321)
638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF -
From Promise to Prominence: Celebrating 40 Years