Re: [EnergyPlus_Support] multi-zone control strategy
How you set this up depends on the type of system you use.
If you are simply using a heating coil in an air loop, place the
thermostat in Zone 2 and use a single zone heating set point manager to
set the heating coil outlet node set point when the fan is before the
heating coil. If the fan is after the heating coil, put the set point
from the single zone heating set point manager at the outlet of the fan
and use a mixed air set point manager to adjust the set point at the
outlet of the fan to account for fan heat. The mixed air set point will
be placed at the heating coil outlet node.
If you are using a unitary system or furnace, simple using a thermostat
in Zone 2 will work.
junu_lee wrote:
>
> I want to simulate the following control strategy:
>
> There are four zones (Zone 1, 2, 3, 4) in my model.
> I want to make heat supply to zone 1, 3, 4 be determined by zone 2
> temperature.
> I would appreciate it if you could let me know how to simulate it.
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/