Re: [EnergyPlus_Support] Simulation using outdoor air and fully exhaust fan
The heat cool furnace uses a separate heating and reheat coil only to
keep the heating and reheat load separate for reporting purposes. A real
system would have only 1 heating coil. The heating coil reports
specifics due to a heating load, and the reheat coil reports specifics
due to dehumidification. The heat cool furnace is used an conjunction
with an outdoor air mixer and an associated outdoor air controller to
specify the outside air requirements. You would probably use the
constant volume fan and would not need the exhaust fan since the outdoor
air mixer/controller takes care of the exhaust air. The zone ventilation
object is used for wind driven ventilation and is not needed for your
application. You can, however, add it if you need it (there is usually
some form of non-mechanical ventilation or infiltration in every building)..
Abdul Murad Zainal Abidin wrote:
>
>
> Hello,
>
> I have a couple of questions:
>
> 1. Can reheat processes be simulated by only using cooling coil and
> heater coil? I have seen in the input-output reference for
> AirloopHVAC:Furnace:HeatCool where there is one cooling coil, heater
> coil and a reheat coil. What is the purpose of having the heater coil?
>
> 2. I intend to use 100% outdoor air for cooling, dehumidify and reheat
> before it enters a zone. Then, I want to fully exhaust the air. Do I
> need to have inputs in the following?
>
> Zone Airflow:
> ZoneVentilation
>
> Controller: OutdoorAir
>
> Fan:ConstantVolume
> Fan:ZoneExhaust
>
>
> Thank you for reading.
>
> Murad
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/