Re: [EnergyPlus_Support] Cooling load - simulation crash - help



It looks like your simulation is crashing because of the tabular 
reports. There are more than 1000 columns. My guess is it has to do with 
this report request: Try deleting this object and run the simulation again.

Output:Table:Monthly,
Surface ext Temperatures,!- Name
2, !- Digits After Decimal
Surface Outside Temperature, !- Variable or Meter 1 Name
SumOrAverage, !- Aggregation Type for Variable or Meter 1
Surface Outside Temperature, !- Variable or Meter 2 Name
Maximum, !- Aggregation Type for Variable or Meter 2
Surface Outside Temperature, !- Variable or Meter 3 Name
Minimum; !- Aggregation Type for Variable or Meter 3


Theodoridou Ifigeneia wrote:
>
>
> Thank u for the instant response!
>
> I could ignore the warnings, but the problem is the error is fatal, 
> the simulation crashes and I am getting no results...
>
> I have run the same file (the same inputs with the dual setpoint) for 
> an other building and it didnt crash. It doesnt make sence...
>
> O/H Richard Raustad ??????:
>
>> The warnings are just telling you the cooling loads in those zones are 
>> 0, but you already know that since there is no cooling system.
>>
>> Does the thermostat use a "dual set point", or just a "single heating" 
>> set point?
>>
>> If you are using a dual set point, change it to single heating set point 
>> and see if the warnings disappear. If that doesn't help, just ignore the 
>> warnings.
>>
>> If you are using a single heating set point, you can ignore these warnings.
>>
>> ifigeneiat wrote:
>>   
>>> Dear all,
>>>
>>> I am having a hard time with an idf file imported from DB. It only has 
>>> a heating system (baseboards). The simulation is running, all 
>>> branches, nodes etc. passed the control, but when coming to the 
>>> "running E+ simulation – SUMMER DESIGN DAY" it crashes! The error 
>>> message says that the cooling loads of my heated zones are equal to zero.
>>> How do I solve this? I never asked for E+ to calculate any of this and 
>>> no cooling system is on.
>>>
>>> Thanx in advance!
>>>
>>> ifigeneia
>>>
>>>
>>>     
>>
>>   
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/