It currently uses a really old ASHRAE clearsky model, hopefullly you can read Fortran:

         IF(CosZenith >= SunIsUpValue) THEN
           ! Sun is up.  Calculate solar values
           TotHoriz = DesDayInput(EnvrnNum)%SkyClear * A * (C + CosZenith) * EXP( -B / CosZenith)
           HO=GlobalSolarConstant*AVSC*CosZenith
           KT=TotHoriz/HO
           KT=MIN(KT,.75d0)
           Wthr%DifSolarRad(Hour) = TotHoriz * (1.0045d0 + KT * (.04349d0 + &
                                                    KT * (-3.5227d0 + 2.6313d0 * KT)))
           IF (DesDayInput(EnvrnNum)%SkyClear .GT. 0.70d0)    &
                     Wthr%DifSolarRad(Hour) = TotHoriz*C/(C+CosZenith)
           Wthr%BeamSolarRad(Hour) = &
                                (TotHoriz-Wthr%DifSolarRad(Hour))/CosZenith
           Wthr%DifSolarRad(Hour) = MAX(0.0d0,Wthr%DifSolarRad(Hour))
           Wthr%BeamSolarRad(Hour) = MAX(0.0d0,Wthr%BeamSolarRad(Hour))
         ELSE

when the sun is not up -- these are set to 0.0