Hi, Natassa
The followings are in your .rdd file after simulation.
HVAC,Average, Ground Heat Exchanger Average Borehole Temperature[ C]
HVAC,Average, Ground Heat Exchanger Heat Transfer[W]
HVAC,Average, Ground Heat Exchanger Inlet Temp[C]
HVAC,Average, Ground Heat Exchanger Outlet Temp[C]
HVAC,Average, Ground Heat Exchanger Mass Flow Rate[kg/s]
HVAC,Average, Ground Heat Exchanger Average Fluid Temp[C]
HVAC,Average, GSHP Electric Power [W]
HVAC,Average, GSHP Load Side Heat Transfer Rate [W]
HVAC,Average, GSHP Source Side Heat Transfer Rate [W]
HVAC,Average, GSHP Load Side Outlet Temperature [°C]
HVAC,Average, GSHP Load Side Inlet Temperature [°C]
HVAC,Average, GSHP Source Side Outlet Temperature [°C]
HVAC,Average, GSHP Source Side Inlet Temperature [°C]
HVAC,Average, GSHP Load Side Water Mass Flow Rate[kg/s]
HVAC,Average, GSHP Source Side Water Mass Flow Rate[kg/s]
Have you looked at these?
Dr. Li
To: EnergyPlus_Support@ yahoogroups. com
From: natamats@yahoo. com
Date: Sat, 13 Feb 2010 11:44:02 -0800
Subject: Re: [EnergyPlus_ Support] Need help with this idf
Hello,
Can somebody please tell me how can i find the consumption of electric energy and the heat transfer from the ground?
Thank you,
Natassa
From: Natassa Matsota <natamats@yahoo. com>
To: EnergyPlus_Support@ yahoogroups. com
Sent: Thu, February 11, 2010 1:02:05 PM
Subject: Re: [EnergyPlus_ Support] Need help with this idf
Hello Linda,
which field i have to change in order to correct this mistake because i can t figure it out?
Thank you,
Natassa
From: Linda Lawrie <linda@fortlawrie. com>
To: EnergyPlus_Support@ yahoogroups. com
Sent: Tue, February 9, 2010 6:16:44 PM
Subject: Re: [EnergyPlus_ Support] Need help with this idf
Your error:
** Warning ** Check GLHE design inputs & g-functions for consistency
** Fatal ** FOR GROUND HEAT EXCHANGER:VERTICAL VERTICAL GROUND HEAT EXCHANGERGLHE delta Temp > 100C.
Did you do that?
If you can't figure it out, please contact the helpdesk with your input file.
Send email to EnergyPlus-Support@ gard.com or log into
http://energyplus. helpserve. com
At 09:07 AM 2/9/2010, Natassa Matsota wrote:
Can anybody please take a look and tell me if there are any changes i can make in order for the simulation to proceed? I really need your help.
Thank you,
Natassa