Dear Fernando, Some more thoughts: ·
WaterHeater:Mixed shows an outdoor air node “HPWHPlantTank OA
Node”. This node is not included in your outdoor air NodeList. I do not know
if that’s a problem, though. ·
Your fan is upstream of the DX coil, so it’s different than the
IO Reference example, but I do not think that is a problem. ·
The IO Reference discussion for the for WaterHeater:HeatPump
says, I do not think that you have your nodes connected to the plant loop,
so perhaps that is the problem. I cannot spend more time on this problem today, but I hope that
I have been some small assistance. I am happy to help as time permits! The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Fernando Pinto
da Silva
From: "James V Dirkes II, PE"
<jvd2pe@xxxxxxx> Fernando, I understand
better now. Consider: I do not see any
object which uses the water such as WaterUse:Equipment. If there is no
water use, the load will be zero. In this case,
HPHW Use Inlet Node must be connected to a water use. (I cannot spend
more time on this for several hours. I hope this helps!) WaterHeater:
Mixed Coil: WaterHeater:
HeatPump The Building Performance Team From: EnergyPlus_Support@ yahoogroups. com
[mailto:EnergyPlus_ Support@yahoogro ups.com] On Behalf Of Fernando
Silva
__._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.