It makes sense what you say. But there is a way to make sure you have 100% fresh air, like Mario said. I checked the Input/output reference, and it does say the following (relative to Controller:OutdoorAir, Field: Maximum/Minimum Fraction of Outdoor Air Schedule): "If both the above schedules are given values of 1.0, the system works at 100% outdoor air" For now, i'm just trying to make a simple system working by the most standard way possible, so I can get myself a systematic procedure that assures me adaptability to various situations, so I'll try not to forget the previous point. Anyway, my problem still persists. I added the OutdoorAir:Mixer and the Controller:OutdoorAir but the program still gives me the same error: Severe ** Demand Side Outlet Node Name (Return Air Path or ZoneHVAC:EquipmentConnections) not valid = ZONE EQ1 OUTLET NODE ~~~ ** Occurs in AirLoopHVAC = UTANN This node is defined as the outlet node of the AirLoopHVAC:ZoneMixer and the Demand Side Outlet Node in AirLoopHVAC. Still need some tips-and-tricks to solve this one. thanks! Pedro P. To: energyplus_support@xxxxxxxxxxxxxxx From: yli006@xxxxxxxxxxx Date: Wed, 2 Jun 2010 13:13:37 -0400 Subject: RE: [EnergyPlus_Support] Air Exhaust from zones problem
I have seen many people wanted to use 100% outside air and does not know what to do.
If your OA intake volume rate is the same as the fan capacity and the zone air flow rate, the return air is automatically relieved, 100%. If you do not connect the return air node of the zone to the OA mixer, the zone air is also 100% exhausted to the outside environment. Am I right? Dr. Li To: EnergyPlus_Support@ From: pedro_peixeiro@ Date: Tue, 1 Jun 2010 08:43:12 +0000 Subject: [EnergyPlus_
hello everyone.
i'm doing my first attempts on HVAC simulation, and i've hit my first wall. The system i'm trying to simulate is working with 100% outside air, and thus i need all zone air to be exhausted outside, with no return. My first idea was to use a AirLoopHVAC: Pedro. 30 days of prizes: Hotmail makes your day easier! Enter now The New Busy think 9 to 5 is a cute idea. Combine multiple calendars with Hotmail. Get busy. __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |