|
"If both the above schedules are given values of 1.0, the system works at 100% outdoor air" This statement is not correct, because by setting the multiplier to 1 does not define the quantity of flow. 1 of zero is still zero. My argument was that the intake air must all flow through the fan and the zone and then exhaust to satisfy the 100% fresh air condition. Therefore, you make the OA intake rate,(volume) the same as the fan rate. If the fan is not supplied with the air quantity you want, then what is the 100% you are referring to. Any volume of air that is not supplied by the OA inlet is made up by return air or other means, so that the OA mixer node will satisfy the fan flow requirement, and the 100% fresh air condition is not met. This argument is not system dependent, excep the Fan. If there is no fan, no wind there is no fresh air.. Dr. Li To: energyplus_support@xxxxxxxxxxxxxxx From: pedro_peixeiro@xxxxxxxxxxx Date: Fri, 4 Jun 2010 07:41:17 +0000 Subject: RE: [EnergyPlus_Support] Air Exhaust from zones problem
It makes sense what you say. But there is a way to make sure you have 100% fresh air, like Mario said. I checked the Input/output reference, and it does say the following (relative to Controller:OutdoorA
"If both the above schedules are given values of 1.0, the system works at 100% outdoor air" For now, i'm just trying to make a simple system working by the most standard way possible, so I can get myself a systematic procedure that assures me adaptability to various situations, so I'll try not to forget the previous point. Anyway, my problem still persists. I added the OutdoorAir:Mixer and the Controller:OutdoorA Severe ** Demand Side Outlet Node Name (Return Air Path or ZoneHVAC:EquipmentC ~~~ ** Occurs in AirLoopHVAC = UTANN This node is defined as the outlet node of the AirLoopHVAC: Still need some tips-and-tricks to solve this one. thanks! Pedro P. To: energyplus_support@ From: yli006@hotmail. Date: Wed, 2 Jun 2010 13:13:37 -0400 Subject: RE: [EnergyPlus_ I have seen many people wanted to use 100% outside air and does not know what to do.
If your OA intake volume rate is the same as the fan capacity and the zone air flow rate, the return air is automatically relieved, 100%. If you do not connect the return air node of the zone to the OA mixer, the zone air is also 100% exhausted to the outside environment. Am I right? Dr. Li To: EnergyPlus_Support@ From: pedro_peixeiro@ Date: Tue, 1 Jun 2010 08:43:12 +0000 Subject: [EnergyPlus_ hello everyone.
i'm doing my first attempts on HVAC simulation, and i've hit my first wall. The system i'm trying to simulate is working with 100% outside air, and thus i need all zone air to be exhausted outside, with no return. My first idea was to use a AirLoopHVAC: Pedro. 30 days of prizes: Hotmail makes your day easier! Enter now The New Busy think 9 to 5 is a cute idea. Combine multiple calendars with Hotmail. Get busy. Enter for a chance to get your town photo on Bing.ca! Submit a Photo Now! __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |