Hi, Julian
I do not know why you are choosing PTHP as your system. The system is correctly entered in your IDF. The expidf can be used for simulation without error, but with many warnings to let know that the Heat Pump is not suitable at that location.
The IdealLoadSystem will probably get you all the values you need to design or modify the building. You should not use 'absolue' and 'relative' for your coordinates. The use of DesignBuilder may have confused you.
Your other requirements:
Is considered to install a solar heating system air to provide cooling in summer only, including treatment of humidity, as it is considered that the thermal requirements of heating are negligible.
Heat pump does not work below 5°C, therefore the auxiliary heater was heating your building.
No cooling required at La Molina. You may have chosen a wrong location for your exercise.
In your IDF:
Site:Location,
LA MOLINA, !- Name
42.34, !- Latitude {deg}
1.96, !- Longitude {deg}
1, !- Time Zone {hr}
1932; !- Elevation {m}
At 43.34 latitude and 1932m above sea level, I do not think you can get 24°C all the year around, without heating.
The lighting load is 17W/m2 (30% convective) and a control system on / off. it depends on the external radiation (1600kJ/h.m2 setpoint). ????
Daylighting can be invoked in EnergyPlus by the use of two objects: Daylighting:Controls
and Daylighting:DELight:Controls.
All windows have internal shutters are controlled on / off is switched on or off according to external radiation (setpoint 1600kJ/h.m2 - 450W/m2).
To do this simulation, you will need to add WindowMaterial:Shade (page 124 IO Manual) for your windows, and define a WindowProperty:ShadingControl object, which can use the solar beam to turn the blind slat angle.
Dr. Li
Date: Thu, 28 Oct 2010 05:11:15 -0700
From: julianflorentinos@xxxxxxxxx
Subject: RE: [EnergyPlus_Support] Error
To: yli006@xxxxxxxxxxx
Hello Dr Li,
I have problems to solve this exercise, I leave attached below the data to see them and can guide me to resolve them better. Also I have to get another year to obtain temperatures of 24C ° and constant humidity of 50%. We spent a expidf file to enter the examples there if possible as this is the way to better understand what I should do. As simepre agradesco and respect him very much for your dedication. Greetings. Julian.
--- El mar, 10/26/10, YuanLu Li <yli006@xxxxxxxxxxx> escribió:
De: YuanLu Li <yli006@xxxxxxxxxxx> Asunto: RE: [EnergyPlus_Support] Error A: "Julian Florentinos" <julianflorentinos@xxxxxxxxx> Fecha: martes, 26 de octubre de 2010, 08:33 pm
Hi, Julian I do not think there is any error in the IDF. There was no cooling load, because the highest outdoor temperature is below 20°C, probably because the location is over 1000m above sea level. Dr. Li
Date: Tue, 26 Oct 2010 06:21:28 -0700 From: julianflorentinos@xxxxxxxxx Subject: RE: [EnergyPlus_Support] Error To: yli006@xxxxxxxxxxx
hello Dr Li,
It previously was simulated with weather data for Barcelona but for now enter the Molina, in doing this I get errors:
** Warning ** World Coordinate System selected. Any non-zero, Building / Zone Axes North Zone or non-zero Origins Are ignored. ~ ~ ~ ** ** These May be Used in Calculations Coordinate daylighting reference point But Not in normal geometry inputs. ** Warning ** Calculated design cooling load for zone = zone 1 is zero. ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs. ** Warning ** Calculated design cooling load for
zone = 3Zone is zero. ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs.
How can I fix it?
Greetings and thanks |
|