Re: [EnergyPlus_Support] Simulation errors




Hi!
I did it, i mean i had changed just the surfaces that got problems but the problem was still running.

This is the problem that appeared when i change just the two surfaces which got the initial problem.


Program Version,EnergyPlus 6.0.0.023, 24/02/2011 05:44 p.m.,IDD_Version 6.0.0.023
   ** Warning ** Floor Tilt=90.0, much less than expected tilt of 180, for Surface=VOID SPACE SOUTH, in Zone=ZONE_2
   ** Severe  ** Suspected non-planar surface:"WALL EAST", Max "out of line"=1.02916E-002 at Vertex # 3
   ** Severe  ** Suspected 4-sided but non-rectangular Window, Door or GlassDoor:
   **   ~~~   ** Surface=WINDOWS SOUTH, Diagonal1=39.187, Diagonal2=39.245
   ************* Note that the following warning(s) may/will occur if you have not enclosed your zone completely.
   ** Warning ** Entered Volume entered for Zone="ZONE_2" significantly different from calculated Volume
   **   ~~~   ** Entered Zone Volume value=794.27, Calculated Zone Volume value=265.83, entered volume will be used in calculations.


What can i do?

Jaime Zuluaga M


From: Richard Raustad <RRaustad@xxxxxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Thu, 24 February, 2011 17:21:51
Subject: Re: [EnergyPlus_Support] Simulation errors


You weren't supposed to change them all, just the one's with the warnings.