Vinay:
Check all your inputs. Make sure the plant flow rate is being sized to the same flow rate as the pump and the GLHE. Also, make sure your g-function values are based on that same flow rate as well. This often occurs when there is a mismatched flow rate (the glhe runs for a while, then suddenly stops), so you may want to try running the loop under a constant flow rate, to at least diagnose that this is actually the problem.EdwinOn Thu, Mar 31, 2011 at 15:12, Vinay Devanathan <vinay.devanathan@xxxxxxxxx> wrote:
Has anyone come across this error before?
---------------
** Warning ** GetSpecificHeatGlycol: Temperature is out of range (too low) for glycol specific heat **** ~~~ ** ..Called From:CalcHPCoolingSimple:SourceSideInletTemp Glycol=WATER,Temperature=-10.50** ~~~ ** Environment=WATERTOWN AP ANN HTG 99.6% CONDNS DB, at Simulation time=01/21 00:00 - 00:15** Warning ** Check GLHE design inputs & g-functions for consistency** ~~~ ** For GroundHeatExchanger:Vertical VERTICAL GROUND HEAT EXCHANGERGLHE delta Temp > 100C.** ~~~ ** This can be encountered in cases where the GLHE mass flow rate is either significantly** ~~~ ** lower than the design value, or cases where the mass flow rate rapidly changes.** ~~~ ** Glhe Current Flow Rate=0.329; Glhe Design Flow Rate=0.329-----------------Is there anything that I am doing wrong causes this error? Any possible fix?Hope to hear from someone.Thank you.