[EnergyPlus_Support] Re: Setpoint for LowTemperatureRadiating:ConstantFlow ?



Karen,

looks indeed the perfect way to control, but I can't find where I can put the object I want to control (the Pumpschedule of my cooling).
It's not A3 as this is the schedule of the LowTemperatureTurnOff object.

AvailabilityManager:LowTemperatureTurnOff,
A1 , \field Name
A2 , \field Sensor Node Name
N1 , \field Temperature
A3 ; \field Applicability Schedule Name



Geert

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Karen Walkerman <kwalkerman@...> wrote:
>
> You could try an AvailabilityManager.  It looks like
> AvailabilityManager:LowTemperatureTurnOff might work for you.  Don't forget
> to create the AvailabilityManager:AssignmentList object, AND to specify
> the AvailabilityManager:AssignmentList in the Loop syntax.
> 
> --
> Karen
> 
> On Sat, Apr 30, 2011 at 4:47 PM, Geert Bellens <
> geert.bellens@...> wrote:
> 
> >
> >
> > I've made a model with designbuilder, and a VAV is serving ventilation and
> > some of the necessary heating and cooling.
> >
> > I'm now modeling concrete core cooling (and heating) in E+ with the
> > LowTemperatureRadiating:ConstantFlow object.
> >
> > The temp° of the water is regulated by the outdoor temp°. So far so good.
> >
> > I can schedule the pump and the object, if I want (but not necessary, it's
> > a continuous system).
> >
> > The temperature of the zone with the concrete cooling/heating is working
> > fine, but...
> >
> > Can I put somewhere a setpoint to prevent the interior temperature to
> > become to high (or to low)caused by the lowtempradiating object ?
> > This means the pump, or the object needs to stop working (for that zone)
> > based on the operating temperature inside ?
> >
> > Geert
> >
> >  
> >
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/