|
E+ calculates dew point temperature internally. You can calculate the zone dew point temp from zone W using this formula. Output:Variable, ZoneName, System Node Humidity Ratio, detailed; Output:Variable, OutdoorNodeName, System Node Pressure, detailed; . . WW = humidity ratio (kg/kg) Pb = 101325.0 !- barometric pressure (Pa), use outdoor pressure RR = Pb*WW/(0.62198+WW) !- RR is temporary variable since this is long equation RR = LN(RR) !- natural logarithm of RR DDP = (-35.957-1.8726*RR+1.1689*RR**2) !- dew point (C) On 8/1/2011 7:31 AM, Jean marais wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |