I do not know why you have the question on the designDay simulation now.
You can have as many designDay objects in the IDF as you wish. For a large building zone model, the simulation may take a long time for each warmup step. On my slow PC, your model took about 2 minutes per warm up step. It ran for about 40 steps, 20 for Summer and 20 for Winter. the total simulation time was more than 1.5 hours.. If you watch the DOS screen, the building warm-up is done first, then the design days warm-up which has [1], etc in the counter. There will be one group of these per designDay object. Because the dates in the designDay can be the same in the same group, you will find the dates repeated for all the Summer and all the Winters. I purposely change thise dates or the day types, so that the results will be easier to separate. ========================== Yes, !- Do the design day calculation No;!- Do the weather file calculation appeared in your question below. =============================== Yes, !- Run Simulation for Sizing Periods No; !- Run Simulation for Weather File Run Appeared in my IDF. The sizing periods can use weather file. There may be some changes which I am not aware of. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: jeannieboef@xxxxxxxxx Date: Wed, 31 Aug 2011 13:56:31 +0000 Subject: [EnergyPlus_Support] Re: How to run DesignDay simulations - Summer and Winter
When I comment out SizingPeriod:DesignDay, Summer Design Day, my other SizingPeriod:DesignDay, Winter Design Day (the remaining one) gets simulated. I get results for the entire day after the simulation (which starts only after sizing and a proper building warmup). I assume this amounts to "design day calculation" specified in the SimulationControl object?
SimulationControl, Yes, !- Do the zone sizing calculation Yes, !- Do the system sizing calculation Yes, !- Do the plant sizing calculation Yes, !- Do the design day calculation No; !- Do the weather file calculation The question is how do I do both of these special designday simulations? Obviously if the one follows the other, I will get 2 days worth of results...will a building warmup take place between them also? Like I said I'm not using runperiod objects. __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |