|
Dear Dr. Li, I agree that you should not need the DX coil in cold weather months! The situation seems to be that: a) A startup condition (when the zone is too warm) causes E+ to use the DX cooling coil for a little while, or b) In the dehumidification scenario I described earlier (when the zone is too humid), it also starts the DX coil I have made my first attempt at using EMS Application guide (below), using example #10 in the EMS as my starting point. It looks like I should be able to override the coil’s availability schedule, but I must be missing something, because it has no effect. Will one of you EMS users please take a look? p.s., I tried both “BeginNewEnvironment” and “InsideHVACSystemIterationLoop” as calling points; same result !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:SENSOR =========== EnergyManagementSystem:Sensor, OutdoorTemp, !- Name Environment, !- Output:Variable or Output:Meter Index Key Name Outdoor Dry Bulb; !- Output:Variable or Output:Meter Name !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:ACTUATOR =========== EnergyManagementSystem:Actuator, DXLowLimit1, !- Name SchCpct_LowTempClgOFF, !- Actuated Component Unique Name Schedule:Compact, !- Actuated Component Type Schedule Value; !- Actuated Component Control Type !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:PROGRAMCALLINGMANAGER =========== EnergyManagementSystem:ProgramCallingManager, DXLowLimit Management1, !- Name BeginNewEnvironment, !- EnergyPlus Model Calling Point DXCoilControl; !- Program Name 1 !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:PROGRAM =========== EnergyManagementSystem:Program, DXCoilControl, !- Name IF (OutdoorTemp < 15.0), !- Program Line 1 SET DXLowLimit1 = 0.0, !- Program Line 2 ELSE, !- A4 SET DXLowLimit1 = Null, !- A5 ENDIF; !- A6 !- =========== ALL OBJECTS IN CLASS: SCHEDULE:COMPACT =========== Schedule:Compact, SchCpct_LowTempClgOFF, !- Name On/Off, !- Schedule Type Limits Name Through: 12/31, !- Field 1 For: AllDays, !- Field 2 Until: 24:00, !- Field 3 1; !- Field 4 Coil:Cooling:DX:SingleSpeed, ClgCoil1_MainFlrDOAS, !- Name SchCpct_LowTempClgOFF, !- Availability Schedule Name 91377, !- Rated Total Cooling Capacity {W} 0.7, !- Rated Sensible Heat Ratio 3.46, !- Rated COP {W/W} 3.9172, !- Rated Air Flow Rate {m3/s} , !- Rated Evaporator Fan Power Per Volume Flow Rate {W/(m3/s)} NodeOut_MA_MainFlrDOAS, !- Air Inlet Node Name NodeOut_ClgCoil1Air_MainFlrDOAS, !- Air Outlet Node Name DXCoil_Cap-FT_MainFlrDOAS, !- Total Cooling Capacity Function of Temperature Curve Name DXCoil_Cap-FF_MainFlrDOAS, !- Total Cooling Capacity Function of Flow Fraction Curve Name DXCoil_EIR-FT_MainFlrDOAS, !- Energy Input Ratio Function of Temperature Curve Name DXCoil_EIR-FF_MainFlrDOAS, !- Energy Input Ratio Function of Flow Fraction Curve Name DXCoil PLF_MainFlrDOAS; !- Part Load Fraction Correlation Curve Name The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of YuanLu Li If you have high internal load and the out door air is at -12°C, why do you need the Dx coil? To: EnergyPlus_Support@xxxxxxxxxxxxxxx Jim, I totally agree with you. Outdoor drybulb minimum limit control is on the list of high-priority development items. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Jim Dirkes Dear Chandan, Brent, Jean, Thanks for the feedback! I must say, though, that I was hoping to avoid learning EMS for maybe 30 years or so… Perhaps this is actually a development issue, but I thought about this a bit more and would like to know your thoughts in response: The normal warning I receive is shown below and is quite understandable. Occasionally a DX coil “wants” to start to satisfy a cooling load in cool weather due to high internal loads, or (as is my case) it may be a DOAS with hot gas reheat and is trying to dehumidify a humid zone. Both uses are legitimate. Both will result in a lot of warnings. In the first case, I can live with a slight increase in the zone temperature during those hours. In the second case, the zone humidity will probably drop once the air system operates for a while (my DOAS was trying to dehumidify in the first few hours after startup) Most commercial HVAC equipment, however, is equipped with a low temperature limit control for the DX cooling that prevents its operation below a fixed temperature. It sure would make an energy modeler’s life more simple if I could just turn the coil OFF with a standard object field instead of EMS! (something like the feature that already exists for the Heat Pump DX heating coil) ** Warning ** Coil:Cooling:DX:SingleSpeed "CLGCOIL1_PROPDOASWVRF0" - Full load outlet air dry-bulb temperature < 2C. This indicates the possibility of coil frost/freeze. Outlet temperature = 1.77 C. ** ~~~ ** ...Occurrence info = FOURPOINTSSHERATON, 01/01 06:18 - 06:20 ** ~~~ ** ... Possible reasons for low outlet air dry-bulb temperatures are: This DX coil ** ~~~ ** 1) may have a low inlet air dry-bulb temperature. Inlet air temperature = 12.200 C. ** ~~~ ** 2) may have a low air flow rate per watt of cooling capacity. Check inputs. ** ~~~ ** 3) is used as part of a HX assisted cooling coil which uses a high sensible effectiveness. Check inputs. The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Chandan Sharma Dear Mr. Dirkes, Dear Dr. Li, I understand that part. I’m trying to turn off the COOLING coil below ~13C. The Building Performance Team __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |