|
After the correcting the error spotted by Karen, the following is the only one that may need correction.
Controller:WaterCoil,
The reason for high temperature at night in Summer was due to internal load (>10kW). You should try to vent these heat out directly rather then cooling it with air-conditioning in Summer. Vent out in Summer and retain the heat for Winter.
Computer equipment is now less than 100w per unit. How many do you have in the room? Printer, etc. have a sleep mode.
Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: matthew.sverre.anderson@xxxxxxxxx Date: Mon, 14 Nov 2011 19:16:40 +0000 Subject: [EnergyPlus_Support] Re: IDF Review for no Cooling
I am currently doing some other things at work and will try that a little later. Is that why there is no cooling occurring in this IDF?
Is there anyway you could troubleshoot the IDF Dr. Li? --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, YuanLu Li <yli006@...> wrote: > > > You can set a wider dead band for the un-occupied period. Heating set point must be lower than the cooling set point, so that they do not overlap. The dead band may be as little as 0.1°F. Otherwice, you can set them to any temperature. If I wanted to turn off the cooling completely, I simply set the cooling set point to 98°F for that zone. If you have water system, you may still need the seasonal control for the plants., so that the water system will be freeze. > > Dr. Li > To: EnergyPlus_Support@xxxxxxxxxxxxxxx > From: matthew.sverre.anderson@... > Date: Mon, 14 Nov 2011 18:39:01 +0000 > Subject: [EnergyPlus_Support] Re: IDF Review for no Cooling > > > > > > > > > > > > > > > > > > > > > > > > > > > > > So do something like set a cooling set point to 74, Heating to 70 for a mean set point of 72 with a 2 degree deadband? > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jean marais" <jeannieboef@> wrote: > > > > > > HEATING COOLING SETPOINTS is the schedule name for both your heating setpoint and your cooling setpoint. I recommend using 2 seperate schedules to achieve a dead band. > > > > __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |