The thermostat temperature schedules should not use setback/setup during sizing periods (i.e., SummerDesignDay and WinterDesignDay temperature set point should be constant) so that the autosized flow rate is not excessively high. Then during the actual simulation, when a setback/setup temperature schedule IS used, the peaks during "thermostat temperature set up" may not be as high. Schedule:Compact, Htg-SetP-Sch, !- Name Temperature, !- Schedule Type Limits Name Through: 12/31, !- Field 1 For: Weekends HoliDay, !- Field 2 Until: 7:00,12.8, !- Field 3 Until: 14:00,21.1, !- Field 5 Until: 24:00,12.8, !- Field 7 For: SummerDesignDay, !- Field 9 Until: 24:00,12.8, !- Field 10 For: WinterDesignDay, !- Field 12 Until: 24:00,21.1, !- Field 13 For: AllOtherDays, !- Field 15 Until: 7:00,12.8, !- Field 16 Until: 19:00,21.1, !- Field 18 Until: 24:00,12.8; !- Field 20 Schedule:Compact, Clg-SetP-Sch, !- Name Temperature, !- Schedule Type Limits Name Through: 12/31, !- Field 1 For: Weekends HoliDay, !- Field 2 Until: 7:00,40.0, !- Field 3 Until: 14:00,23.9, !- Field 5 Until: 24:00,32.2, !- Field 7 For: SummerDesignDay, !- Field 9 Until: 24:00,23.9, !- Field 10 For: WinterDesignDay, !- Field 12 Until: 24:00,40.0, !- Field 13 For: AllOtherDays, !- Field 15 Until: 7:00,40.0, !- Field 16 Until: 19:00,23.9, !- Field 18 Until: 24:00,40.0; !- Field 20 On 11/21/2011 4:31 PM, YuanLu Li wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |