After running your IDF, I found that you have many unusual features.
The DesignDay temperature range is zero. The temperature is constant for the whole day. Infiltratin is very high, so that Winter cold air and Summer hot air are added to your load. You have very high internal load in Summer. Therefore high cooling rate. Check the schedule for Winter. Window heat gain and loas are in the order of 5kw each This adds to your heating and cooling load. Ground temperature was not endered and assumed to be 18°C. This is keeping your zone temperature high in Winter. No heating required at night. (higher than 10°C) ========================= I have change some of the schedules and designDay data, and report variables to test the simulation. The infiltration is turned off, and the DesignDay data is from the .ddy file. OA minimum fow is also zero. The heating and cooling rate are now accountable. the .csv and .idf are attached. ==================== If you are learning to design the building do not use fancy schedules, people, clothings, etc. Make sure that the building is cool in Summer and warm in Winter, and then add a little HVAC to increase comfort. Simulation with different equipment will not improve energy usage. Dr. Li P.S. for Richard Are you saying that if the actual type 4 on/off (high/low) setpoint is used for sizing, the maximum available flow rate would be higher, and a temperature change can be met faster. When the peak flow is limited, the fast temperture rise becomes a rounded temperature rise in the simulation, as in most VAV cases. To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: RRaustad@xxxxxxxxxxxx Date: Mon, 21 Nov 2011 16:42:40 -0500 Subject: Re: [EnergyPlus_Support] Re: Problem with results of a simulation
The thermostat temperature schedules should not use setback/setup
during sizing periods (i.e., SummerDesignDay and WinterDesignDay
temperature set point should be constant) so that the autosized flow
rate is not excessively high. Then during the actual simulation,
when a setback/setup temperature schedule IS used, the peaks during
"thermostat temperature set up" may not be as high.
Schedule:Compact, Htg-SetP-Sch, !- Name Temperature, !- Schedule Type Limits Name Through: 12/31, !- Field 1 For: Weekends HoliDay, !- Field 2 Until: 7:00,12.8, !- Field 3 Until: 14:00,21.1, !- Field 5 Until: 24:00,12.8, !- Field 7 For: SummerDesignDay, !- Field 9 Until: 24:00,12.8, !- Field 10 For: WinterDesignDay, !- Field 12 Until: 24:00,21.1, !- Field 13 For: AllOtherDays, !- Field 15 Until: 7:00,12.8, !- Field 16 Until: 19:00,21.1, !- Field 18 Until: 24:00,12.8; !- Field 20 Schedule:Compact, Clg-SetP-Sch, !- Name Temperature, !- Schedule Type Limits Name Through: 12/31, !- Field 1 For: Weekends HoliDay, !- Field 2 Until: 7:00,40.0, !- Field 3 Until: 14:00,23.9, !- Field 5 Until: 24:00,32.2, !- Field 7 For: SummerDesignDay, !- Field 9 Until: 24:00,23.9, !- Field 10 For: WinterDesignDay, !- Field 12 Until: 24:00,40.0, !- Field 13 For: AllOtherDays, !- Field 15 Until: 7:00,40.0, !- Field 16 Until: 19:00,23.9, !- Field 18 Until: 24:00,40.0; !- Field 20 On 11/21/2011 4:31 PM, YuanLu Li wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.