There is nothing really wrong with the IDF.
You have infiltration to give you the air flow rate. 200kW cooling rate and 15kw heating rate is normal, for the two zones side by side with many windows. Simplify or display your schedule values, and you will understand what is happening. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: RRaustad@xxxxxxxxxxxx Date: Mon, 21 Nov 2011 16:42:40 -0500 Subject: Re: [EnergyPlus_Support] Re: Problem with results of a simulation
The thermostat temperature schedules should not use setback/setup
during sizing periods (i.e., SummerDesignDay and WinterDesignDay
temperature set point should be constant) so that the autosized flow
rate is not excessively high. Then during the actual simulation,
when a setback/setup temperature schedule IS used, the peaks during
"thermostat temperature set up" may not be as high.
Schedule:Compact, Htg-SetP-Sch, !- Name Temperature, !- Schedule Type Limits Name Through: 12/31, !- Field 1 For: Weekends HoliDay, !- Field 2 Until: 7:00,12.8, !- Field 3 Until: 14:00,21.1, !- Field 5 Until: 24:00,12.8, !- Field 7 For: SummerDesignDay, !- Field 9 Until: 24:00,12.8, !- Field 10 For: WinterDesignDay, !- Field 12 Until: 24:00,21.1, !- Field 13 For: AllOtherDays, !- Field 15 Until: 7:00,12.8, !- Field 16 Until: 19:00,21.1, !- Field 18 Until: 24:00,12.8; !- Field 20 Schedule:Compact, Clg-SetP-Sch, !- Name Temperature, !- Schedule Type Limits Name Through: 12/31, !- Field 1 For: Weekends HoliDay, !- Field 2 Until: 7:00,40.0, !- Field 3 Until: 14:00,23.9, !- Field 5 Until: 24:00,32.2, !- Field 7 For: SummerDesignDay, !- Field 9 Until: 24:00,23.9, !- Field 10 For: WinterDesignDay, !- Field 12 Until: 24:00,40.0, !- Field 13 For: AllOtherDays, !- Field 15 Until: 7:00,40.0, !- Field 16 Until: 19:00,23.9, !- Field 18 Until: 24:00,40.0; !- Field 20 On 11/21/2011 4:31 PM, YuanLu Li wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.