To be exactly correct you should divide the operating power by the full load capacity at the specific operating condition. This would be: EIRfPLR = Pactual / (Capacity at 100% x CAPFT) / EIR at 100% AT PLR =1, CAPFT = 1, and EIR at 100% is the same as Pactual / Capacity at 100% so at PLR = 1, EIRfPLR = 1 Have a nice weekend, over and out. On 2/10/2012 2:44 PM, Nacho Gomis wrote: I think I didn't understand this part of the email you wrote me: -- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.