[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff







From: YuanLu Li <yli006@xxxxxxxxxxx>
To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx>
Sent: Tuesday, February 21, 2012 10:15 PM
Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
 
Dr.Li :
in the building that i simulated :The real building or the IDF? 
 real building
 
 
 
 
the thermostat of boiler ( aquastat ) switch on/off the burner , and the thermostat surface on the main return pipe hot water loop that it controls hot water pump (HW pump ) and another thermostat on the domostic hot water pipe of coil tank for domostic hot water that controls when water of in the coil needs heat
 
 
 
 
 
 
If these are on your real building, they are thermometers, and do not do any controlling.
 
no there are nt thermometr , there are thermostat ,
thermometr just measured tempersture but thermostat conrols temperature,
 
If these are in the IDF, they should be properly entered with the correct names, controllers and managers.  They are not necessary, as the boiler thermostat will do all these for you.
 Dr.Li ,  what is boiler thermostat in energyplus ?is this design outlet water temperature  in boiler class ? you mean when i enter  design outler water temperature: 80 , it means when outlet boiler temperature is greater than 80 then boiler will be off and when less than 80 it will be on ?it doesn have any deadband?
You will not be able to use the set point managers and EMS, if you cannot distinguish a thermometer from a thermostat function.
i know what is different between thermostat and thermometer , thermometr just measured the temperature of that node , but themostat controls the temperature ,
 
I kept saying that you need not control the pump in the EPlus simulation, and you insist that it must stop at  80°C and start at 65°C and turn on and off the boiler fire.  The system does not operate in your way.
 
  i say boiler will be on and off with its temperature of burner ( if greater than 8o boiler will be off , and if less than 75 will be on , 5 is its deadband) and i say hw pumo contrl with its own thermostat that install in the return hot water pipe ,
You e-mail below showed a DHW schedule which is on all the time except at 3am.  That was why I said that your pump will not turn off.  You have not proved that the schedule was actually working in your IDF.
 yes i know that , in my schedule the domostic hot water for 3 am is 0 then DHW pump will be off , but i talk about hw pump controll
 
Showing me some isolated schedules and objects will not help.
 
 Dr. Li  

 
To: EnergyPlus_Support@xxxxxxxxxxxxxxxFrom: t.t111ir@xxxxxxxxxDate: Tue, 21 Feb 2012 15:05:54 +0000Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff 


From: YuanLu Li <yli006@xxxxxxxxxxx>
To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx>
Sent: Monday, February 20, 2012 9:51 PM
Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
 
An intermitent pump in EPlus is one which can be switched on and off.    The pump itself does not sense the flow rate, the pressure or the temperature.  It is switched on/off by another controller. could you please describe more little about what controller?
  It may turn itself off, if the pressure is too high for safety reasons.  This is why you have a by-pass branch in the loop.    The thermostat turns off the burner.
the zone air thermostat turn off the burner?  It should not turns off the pump at the same time, unless the pump has a by-pass.   I do not know what switches it off in your real system.
 Dr.Li : in the building that i simulated : the thermostat of boiler ( aquastat ) switch on/off the burner , and the thermostat  surface  on the main return pipe  hot water loop that it controls    hot water pump (HW pump ) and another thermostat on the  domostic hot water pipe of  coil tank for domostic hot water that controls when water of  in the coil needs heat
 
     Dr. Li    
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Mon, 20 Feb 2012 18:11:21 +0000 Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff 
Dr.Li can you say what does  intermitent  pump in energyplus?
the pump will run at its capacity if a load is sensed and will shut off if  there is no load on loop ,
 can you explain it please ?
 


From: YuanLu Li <yli006@xxxxxxxxxxx>
To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx>
Sent: Monday, February 20, 2012 9:36 PM
Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
 
    You have some input to the IDF for the DHW usage.  I have no idea whether it is running or not in the simulation.   Please do not show me a spread sheet for  some measured results, and theb link my comments for the spread sheet to the simulation that I do not know.    Dr. Li    
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Mon, 20 Feb 2012 17:02:33 +0000 Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff 
Dear Dr.Li ,
  i dont undrestandt  you said i was not using the DHW,
i  use :
 
 
 
Schedule:Compact,
    Sinks Flow Schedule,     !- Name
    Any Number,              !- Schedule Type Limits Name
    THROUGH: 12/31,          !- Field 1
    FOR: AllDays,            !- Field 2
    UNTIL: 1:00, 0.003,      !- Field 4
    UNTIL: 2:00, 0.001,      !- Field 6
    UNTIL: 3:00, 0,          !- Field 8
    UNTIL: 4:00, 0,          !- Field 10
    UNTIL: 5:00, 0.001,      !- Field 12
    UNTIL: 6:00, 0.028,      !- Field 14
    UNTIL: 7:00, 0.105,      !- Field 16
    UNTIL: 8:00, 0.1,        !- Field 18
    UNTIL: 9:00, 0.081,      !- Field 20
    UNTIL: 10:00, 0.059,     !- Field 22
    UNTIL: 11:00, 0.051,     !- Field 24
    UNTIL: 12:00, 0.037,     !- Field 26
    UNTIL: 13:00, 0.031,     !- Field 28
    UNTIL: 14:00, 0.026,     !- Field 30
    UNTIL: 15:00, 0.023,     !- Field 32
    UNTIL: 16:00, 0.033,     !- Field 34
    UNTIL: 17:00, 0.041,     !- Field 36
    UNTIL: 18:00, 0.063,     !- Field 38
    UNTIL: 19:00, 0.075,     !- Field 40
    UNTIL: 20:00, 0.066,     !- Field 42
    UNTIL: 21:00, 0.059,     !- Field 44
    UNTIL: 22:00, 0.046,     !- Field 46
    UNTIL: 23:00, 0.046,     !- Field 48
    UNTIL: 24:00, 0.025;     !- Field 50
 
  ===========  ALL OBJECTS IN CLASS: WATERUSE:EQUIPMENT ===========
WaterUse:Equipment,
    Sinks,                   !- Name
    Sinks,                   !- End-Use Subcategory
    0.000158,                !- Peak Flow Rate {m3/s}
    Sinks Flow Schedule,     !- Flow Rate Fraction Schedule Name
    Sinks and Showers Temp Schedule;  !- Target Temperature Schedule Name

!-   ===========  ALL OBJECTS IN CLASS: WATERUSE:CONNECTIONS ===========
WaterUse:Connections,     Domestic Hot Water,      !- Name     Domestic Hot Water Inlet Node,  !- Inlet Node Name     Domestic Hot Water Outlet Node,  !- Outlet Node Name     ,                        !- Supply Water Storage Tank Name     ,                        !- Reclamation Water Storage Tank Name     ,                        !- Hot Water Supply Temperature Schedule Name     ,                        !- Cold Water Supply Temperature Schedule Name     NONE,                    !- Drain Water Heat Exchanger Type     ,                        !- Drain Water Heat Exchanger Destination     ,                        !- Drain Water Heat Exchanger U-Factor Times Area {W/K}     Sinks;                   !- Water Use Equipment 1 Name
 
Schedule:Compact,
    Sinks and Showers Temp Schedule,  !- Name
    Any Number,              !- Schedule Type Limits Name
    THROUGH: 12/31,          !- Field 1
    FOR: AllDays,            !- Field 2
    UNTIL: 24:00, 40.56;     !- Field 4
 
 with this input i think i used DHW , and also i put :
 
PlantEquipmentOperation:HeatingLoad,
    DHW Control Scheme,      !- Name
    0,                       !- Load Range 1 Lower Limit {W}
    90000,                !- Load Range 1 Upper Limit {W}
    DHW Plant Equipment;     !- Range 1 Equipment List Name
PlantEquipmentOperation:HeatingLoad,
    Central Boiler Only,     !- Name
    0,                       !- Load Range 1 Lower Limit {W}
    90000,                 !- Load Range 1 Upper Limit {W}
    heating plant;           !- Range 1 Equipment List Name
 
Dr.Li can you say what does  intermitent  pump in energyplus?
the pump will run at its capacity if a load is sensed and will shut off if  there is no load on loop ,
 can you explain it please ?
 
 
 
From: YuanLu Li <yli006@xxxxxxxxxxx>
To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx>
Sent: Monday, February 20, 2012 7:09 PM
Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
 
That was because you were not using the DHW, and you have 1 mega watt of furnace power.   The boiler furnace does not control the HW pump.  Dr. Li    
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Mon, 20 Feb 2012 13:47:43 +0000 Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff 
it is my experiment data , and i have HW pump off and boiler on
but in my result energyplus i dont have this state , HW pump never off

From: YuanLu Li <yli006@xxxxxxxxxxx>
To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx>
Sent: Monday, February 20, 2012 4:38 PM
Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
 
All four states are on the spread sheet.   Sorry.  I means row 11 an row 12 of the spread sheet..   The year was 2010.  Was it that long ago?  Dr. Li  
Boiler        HW pump  (Starting on row 9)
1 1
1 1
1 0
1 0
0 0    
You missed out this state.
0 1
0 1
1 1
0 1
0 1
1 1
0 1
1 1
0 0
0 0
1 0
1 0
 
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Mon, 20 Feb 2012 00:41:02 +0000 Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff 
excuse me i dont undrestand : on line 11 and 12 " what you mean ?
now in iran is 4:10 AM
From: YuanLu Li <yli006@xxxxxxxxxxx>
To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx>
Sent: Monday, February 20, 2012 4:06 AM
Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
 
On line 11 and 12.  and more later on.  Dr. Li    
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Mon, 20 Feb 2012 00:32:04 +0000 Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff 
Dr.Li sorry for my mistake i dont see the result of HW pump off and boiler on ,
i dont undrestand why , ?
From: YuanLu Li <yli006@xxxxxxxxxxx>
To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx>
Sent: Monday, February 20, 2012 3:55 AM
Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
 
This is why you must not change names and create different names of the objects.   "HW pump" is not the same as "pump" to me.  I do not associate 3 and 4 with the spread sheet as they are only for two other variables.   HW pump on and boiler off is a valid state, because the pump is not controlled by the boiler.   The pump is on the supply side water loop, the boiler fire is on the heating tank source side, and is not in the water loop.  Your statement on EPlus is not correct.  Dr. Li    
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Sun, 19 Feb 2012 23:57:37 +0000 Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff 

From: YuanLu Li <yli006@xxxxxxxxxxx>
To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx>
Sent: Monday, February 20, 2012 3:14 AM
Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
   thanks for looking that
The data looked normal.   You should have taken the temperature values at the same time.   yes i take it but in the excel file that i send you there is nt,
You did not record the DHW pump on the spread sheet.
i  recorded  DHW pump , but in this file that i send you it is only HW pump   HW pump off, boiler off not listed below,
i wrote wrong in number 3, sorry , it must be HW pump off ,boiler off   there is on the spread sheet.
 in my energyplus result i dont see number 4 case (HW pump on and boiler off ) i dont undrestand why?
 ) Hw pump off but boiler on   (DHW is being heated)
2)Hw pump on and boiler on  (Normal )
3)HW pump 0ff but boiler on  (HW below set point, DHW not in use)
4)HW pump on and boiler off  (Tank is hot enough for a while)  i dont this  case result ( HW pump on and boiler off ) in my energyplus result ,
This is an indication that you did not plan the experiment well, and do not record the actual condition on site.   Instead of 0 and 1's on the spread sheet, you should combined the states and then list the meaning of each state.  Two pumps and a boiler fire should give you 8 states.
 yes you are right i have 8 states, but in the excel file that i sent you , there is only the result of HW pump and boiler 
Some states may not be possible, and then your should try to explain them.    Dr. Li    
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Sun, 19 Feb 2012 21:58:35 +0000 Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff 
please see the file that i attached :this is the real experiment data that i measured :
 
it shows some times all of below
1) Hw pump off but boiler on   (DHW is being heated)
2)Hw pump on and boiler on  (Normal )
3)pump 0ff but boiler on  (HW below set point, DHW not in use)
4)pump on and boiler off  (Tank is hot enough for a while)
 
 
 



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___