Re: [EnergyPlus_Support] First time with this software





Mohammad, 
You are doing what I recently figured out.
The time step is kinda an inverse number, so 30 is once per two minutes, 60 is once per minute, 20 once per three minutes.

I have attached files of working PCM models for the BioPCM product line that my project is on, the one titled BioPCM Energy Plus Objects has a data set of working objects that you could plug into your model. 

You say your lab data is measured per 30 minutes, question are you doing isothermal stepped differential scanning calorimetry?

Also note that my PCM model did not converge until I changed the limits to make the tool more stable, and I had to be creative and figure out through a month of experimentation that the internal source sink layer object had to be used in order to show realistic energy savings from PCM's. (The documentation in my opinion does not actually tell you how to create a working model, rather tells about how each feature works)  

To answer your question, use 60 time steps perhour. 

Feel free to email or call me with questions if you get stumped.

Lastly, If you care to share--what material is your PCM, just curios....

Thanks

On Sat, Mar 3, 2012 at 6:26 AM, Linda Lawrie <linda@xxxxxxxxxxxxxx> wrote:
 

I suppose it is your decision -- I am WARNING you that the PCM will have severe inaccuracies in Version 7 with timesteps less than 20.  We are trying to rectify that but not sure we can figure out the cause before the next release.



At 07:14 AM 3/3/2012, Mohammad Kheradmand wrote:


I know why it happen, but i used PCM which it is necessary i put time step 20 , in out put i want to have each 30 minute for temperature. 




--
Jeremiah D. Crossett
CleanTech Analytics
503-688-8951
www.cleantechanalytics.com


This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___
Attachment not found:
d:\eudora\attach\RoomStudy-BioPCM M27-Q21.idf
Attachment not found:
d:\eudora\attach\BioPCM-Energy Plus Objects-V2.idf
Attachment not found:
d:\eudora\attach\RoomStudy-BASELINE.idf