Re: [EnergyPlus_Support] Re: HVAC Terminal Unit: VariableRefrigerantFlow





Hi, Santiago,

I`m working on a VRV system recently, which I try to integrate a VRV system to deal with the sensible load with a ERV to deal with the latent load.

So I wonder how u place 4 units on only 1 Terminal Units, since I cannot find the configuration for capability of TU, except only in the Coil term. However, when I put all the capability on only one coil, all i can get are many severe errors about the rated vol flow per Rated TotCap. So can u give any help about this? Thanks. 

Joey

2012/3/7 iluminasol33 <iluminasol33@xxxxxxxxx>
 

I have solved the problem by reducing the number of terminal units. Before I had 4 TU in one single zone, and this caused many warnings. Now I have placed only 1 TU with the equivalent capacity o the 4 units, and the warnings are gone. But it would be good to be able to insert more than 1 TU per thermal zone. In the meantime I will leave it like this.

Santiago



--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jim Dirkes" <jim@...> wrote:
>
> Santiago,
>
> I am guessing, but I think that "iteration limit exceeded" warnings occur
> when the system heating / cooling capacity is not great enough and also when
> air flow is not balanced between supply and exhaust.
>
> In your example, the load is less than zero, indicating a need for heating
> (-0.12331), but the system is still cooling (although at a very small rate;
> 3.54534E-016). Perhaps this is a cooling-only system? Or several zones are
> included with one system and one of them calls for heating while the others
> need cooling?
>
>
>
> The Building Performance Team
> James V. Dirkes II, P.E., BEMP , LEED AP
> 1631 Acacia Drive NW
> Grand Rapids, MI 49504
> 616 450 8653
>
>
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of iluminasol33
> Sent: Friday, March 02, 2012 7:00 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] HVAC Terminal Unit: VariableRefrigerantFlow
>
>
>
>
>
> Dear Forum,
>
> I started to model the VRV HVAC Terminal Unit, and I have received many
> warnings as this one:
>
> Warning ** ZoneHVAC:TerminalUnit:VariableRefrigerantFlow "TU2 COMEDOR"
> ** ~~~ ** Iteration limit exceeded calculating terminal unit part-load
> ratio, maximum iterations = 500
> ** ~~~ ** Part-load ratio returned = 6.291E-003 Environment=NESTLE CHIAPA DE
> CORZO, at Simulation time=01/02 06:00 - 06:10
> ** ~~~ ** Load requested = -0.12331, Load delivered = 3.54534E-016
>
> I do not know the reason of it, but I think it is necessary to solve it in
> order to trust the results of the simulation.
>
> Any advice greatly appreciated!
>




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___