[EnergyPlus_Support] Re: Preconditioning Air to FCU



I looked through the example file list. There is both a DOAS with FCU and a DOAS with WSHP. However, both of them have OA into zone instead of into the zone unit. 

I thought about attempting to connect the DOAS outlet into the FCU mixing box, but putting a node that isn't an outdoorair:node on the outdoor air inlet would probably kick back an error. 

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jim Dirkes" <jim@...> wrote:
>
> There's not really much difference thermodynamically, Luke.  
> 
> You've got me thinking, though.  I wonder if you can connect the DOAS outlet
> via splitter to the Fan coil OA inlet?  Have you looked for any example
> files which do this?
> 
>  
> 
> The Building Performance Team
> James V. Dirkes II, P.E., BEMP , LEED AP
> 1631 Acacia Drive NW
> Grand Rapids, MI 49504
> 616 450 8653
> 
>  
> 
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of luke_dorna
> Sent: Friday, April 13, 2012 1:34 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Preconditioning Air to FCU
> 
>  
> 
>   
> 
> All,
> 
> I'm working with dedicated outside air unit providing preconditioned air to
> fan coil units in multiple spaces. I noticed the DOAS with FCU template has
> a line for how to input the air, but the only option is direct to zone, and
> not into the unit. 
> 
> Does anyone know how or if it is possible to put a DOAS in series with a fan
> coil in order to provide preconditioned outside air to a unit in the space? 
> 
> Many thanks,
> 
> Luke
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/