It is not going to work to connect the air loop to the back of the fan coil units, but there is development work going on to allow doing that in the future. One option to consider is using the AirTerminal:SingleDuct:ConstantVolume:FourPipeInduction object with the supply air run like a DOAS. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of luke_dorna I looked through the example file list. There is both a DOAS with FCU and a DOAS with WSHP. However, both of them have OA into zone instead of into the zone unit. Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.