Change your file extension to imf (BASELINE-INCLUDE-BioPCM-INP.imf)
and it should work.
Edit RunEPlus.bat to see why you need the imf file extension, this
is what trips EPMacro.exe to run and create the combined input file.
if exist "%input_path%%~1.imf" copy "%input_path%%~1.imf" in.imf
if exist in.imf "%program_path%EPMacro"
if exist out.idf copy out.idf "%output_path%%~1.epmidf"
if exist audit.out copy audit.out "%output_path%%~1.epmdet"
if exist audit.out erase audit.out
if exist out.idf MOVE out.idf in.idf
On 5/13/2012 7:45 PM, CleanTech Analytics wrote:
And when
trying without ! after each (I thought I found the issue was I
was writing to IDD, but did not work)
Again to all
who may know, any advise would be much appreciated. (one thing
I am not sure of is if this has to be ran with command promp?)
again many thanks
Program Version,EnergyPlus-32-MP 7.1.0.009+,
5/13/2012 4:39 PM,IDD_Version 7.1.0.009+
************* IP: IDF Line~15 ##include
C:\Users\Jeremiah\Desktop\INP-EPMACRO\M27.inp
** Severe ** , or ; expected on this line
************* IP: IDF Line~16 ##include
C:\Users\Jeremiah\Desktop\INP-EPMACRO\M51.inp
** Severe ** , or ; expected on this line
************* IP: IDF Line~17 ##include
C:\Users\Jeremiah\Desktop\INP-EPMACRO\M91.inp
** Severe ** , or ; expected on this line
************* IP: IDF Line~18 ##include
C:\Users\Jeremiah\Desktop\INP-EPMACRO\M182.inp
** Severe ** , or ; expected on this line
************* IP: IDF Line~19 ##include
C:\Users\Jeremiah\Desktop\INP-EPMACRO\Q21.inp
** Severe ** , or ; expected on this line
************* IP: IDF Line~20 ##include
C:\Users\Jeremiah\Desktop\INP-EPMACRO\Q23.inp
** Severe ** , or ; expected on this line
************* IP: IDF Line~21 ##include
C:\Users\Jeremiah\Desktop\INP-EPMACRO\Q25.inp
** Severe ** , or ; expected on this line
************* IP: IDF Line~22 ##include
C:\Users\Jeremiah\Desktop\INP-EPMACRO\Q27.inp
** Severe ** , or ; expected on this line
************* Beginning Zone Sizing Calculations
************* Testing Individual Branch Integrity
************* All Branches passed integrity
testing
************* Testing Individual Supply Air Path
Integrity
************* All Supply Air Paths passed
integrity testing
************* Testing Individual Return Air Path
Integrity
************* All Return Air Paths passed integrity
testing
************* No node connection errors were
found.
************* Beginning Simulation
************* Simulation Error Summary
*************
************* EnergyPlus Warmup Error Summary.
During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary.
During Sizing: 0 Warning; 0 Severe Errors.
************* EnergyPlus Completed Successfully--
0 Warning; 8 Severe Errors; Elapsed Time=00hr 03min
26.77sec
Jeremiah D. Crossett
CleanTech Analytics
503-688-8951
This
document may contain valuable information
proprietary to CleanTech Analytics which is private
and confidential. It may not be shared, copied,
stored or transmitted in any form without the prior
written consent of CleanTech Analytics
On Sun, May 13, 2012 at 4:25 PM,
CleanTech Analytics <jeremiah@xxxxxxxxxxxxxxxxxxxxxx>
wrote:
I changed the
file extension to .inp, and followed what seemed to make
since in the documentation but still got the error below
when runing the attached files. Any advise as to what I
am doing wrong?
Many
thanks-
Program Version,EnergyPlus-32-MP 7.1.0.009+,
5/13/2012 4:17 PM,IDD_Version 7.1.0.009+
************* IP: IDF Line~15 ##include
C:\Users\Jeremiah\Desktop\INP-EPMACRO\M27.inp
** Severe ** , or ; expected on this
line
************* Beginning Zone Sizing
Calculations
************* Testing Individual Branch
Integrity
************* All Branches passed
integrity testing
************* Testing Individual Supply
Air Path Integrity
************* All Supply Air Paths
passed integrity testing
************* Testing Individual Return
Air Path Integrity
************* All Return Air Paths passed
integrity testing
************* No node connection errors
were found.
************* Beginning Simulation
************* Simulation Error Summary
*************
************* EnergyPlus Warmup Error
Summary. During Warmup: 0 Warning; 0 Severe
Errors.
************* EnergyPlus Sizing Error
Summary. During Sizing: 0 Warning; 0 Severe
Errors.
************* EnergyPlus Completed
Successfully-- 0 Warning; 1 Severe Errors;
Elapsed Time=00hr 03min 28.84sec
Jeremiah D.
Crossett
CleanTech
Analytics
This document
may contain valuable information
proprietary to CleanTech Analytics which
is private and confidential. It may not be
shared, copied, stored or transmitted in
any form without the prior written consent
of CleanTech Analytics
On Sun, May 13, 2012 at
4:04 PM, CleanTech Analytics <jeremiah@xxxxxxxxxxxxxxxxxxxxxx>
wrote:
Thanks Linda, --
I had looked everywhere but in the
auxiliary programs guide-
Jeremiah D. Crossett
CleanTech Analytics
This
document may contain valuable
information proprietary to
CleanTech Analytics which is
private and confidential. It
may not be shared, copied,
stored or transmitted in any
form without the prior written
consent of CleanTech Analytics
On Sun, May
13, 2012 at 3:51 PM, Linda Lawrie <linda@xxxxxxxxxxxxxx>
wrote:
EP Macro is described
in the Auxiliary
Programs document.
If you are using
EP-Launch, there is a
"inc" that can be set
and tested
in each subsequent
simulation. (I believe
there is a simple
example
shown in the files area
here).
The output files from
EP-Macro are put as
"epmidf" and "epmdet"
extensions -- usually in
the output files area.
It looks like there was
a previous set of
messages about this -- I
will catch up to them
tomorrow.
Linda
On 13.05.2012 16:46,
CleanTech Analytics
wrote:
> Jean,
> Thank you kindly
for the advise;
>
> I have done as you
advised, but I can not
seem to find the output
> tables or csv files
from the macro
simulation.
> I have attached my
files, could you please
help me out and point me
> in
> the right direction
to use the EP Macro
funtonality? My use is
to be
> able to add PCM's
to Energy Plus files in
JE+ runs. I have it
working
> by using 8 IDF's,
but would much rather
use the IMF/EP Macro
> method..
>
> Questions: Should I
use single file, or
group with all IMF's?
Should
> I
> click repeat
simulation for IMF in
the number (8) of IMF
files?
>
> Many thanks
>
> ! File generated by
DesignBuilder -
3.0.0.104 3/18/2012 -
9:46:52 PM
> ! Source file:
C:UsersJeremiahDocumentsDesignBuilder
DataASHRAE Room
> Study.dsb
> Version,
> 7.1;
!- Version
Identifier
>
> ##include
C:UsersJeremiahDesktopBioPCM
IMF'sM27.IMF
>
> !##include
C:UsersJeremiahDesktopBioPCM
IMF'sM51.IMF
>
> !##include
C:UsersJeremiahDesktopBioPCM
IMF'sM91.IMF
>
> !##include
C:UsersJeremiahDesktopBioPCM
IMF'sM182.IMF
>
> !##include
C:UsersJeremiahDesktopBioPCM
IMF'sQ21.IMF
>
> !##include
C:UsersJeremiahDesktopBioPCM
IMF'sQ23.IMF
>
> !##include
C:UsersJeremiahDesktopBioPCM
IMF'sQ25.IMF
>
> !##include
C:UsersJeremiahDesktopBioPCM
IMF'sQ27.IMF
>
> !- ===========
ALL OBJECTS IN CLASS:
SIMULATIONCONTROL
> ===========
>
> Program
Version,EnergyPlus-32-MP
7.1.0.009+, 5/13/2012
3:39
> PM,IDD_Version
7.1.0.009+
> *************
IP: IDF Line~15
##include
>
C:UsersJeremiahDesktopBioPCM
IMF'sM27.IMF
> ** Severe ** ,
or ; expected on this
line
> *************
Beginning Zone Sizing
Calculations
> *************
Testing Individual
Branch Integrity
> *************
All Branches passed
integrity testing
> *************
Testing Individual
Supply Air Path
Integrity
> *************
All Supply Air Paths
passed integrity testing
> *************
Testing Individual
Return Air Path
Integrity
> *************
All Return Air Paths
passed integrity testing
> ************* No
node connection errors
were found.
> *************
Beginning Simulation
> *************
Simulation Error Summary
*************
> *************
EnergyPlus Warmup Error
Summary. During Warmup:
0
> Warning; 0 Severe
Errors.
> *************
EnergyPlus Sizing Error
Summary. During Sizing:
0
> Warning; 0 Severe
Errors.
> *************
EnergyPlus Completed
Successfully-- 0
Warning; 1
> Severe Errors;
Elapsed Time=00hr 03min
36.24sec
>
> _Jeremiah D.
Crossett_
> _CleanTech Analytics_
> _ 503-688-8951_
>
>
_www.cleantechanalytics.com_
[1]
>
> This document may
contain valuable
information proprietary
to
> CleanTech Analytics
which is private and
confidential. It may not
be
> shared, copied,
stored or transmitted in
any form without the
prior
> written consent of
CleanTech Analytics
>
> On Sun, Mar 25,
2012 at 10:23 PM, Jean
marais wrote:
>
>>
>>
>> And to
illistrate...here is a
bit of code epmacro i
used to create
>> the CO2 part
of my idf for the
different zones to
which it must be
>> applied.
>> I ran this
sepperately (still
using eplaunch and
just exchanged the
>> include file
for the CO2 for this
one. It expands into
the CO2 idf
>> that I then
later included...if
that makes sense.
Unfortunately it
>> expands with
a character that has
to be manually removed
with find
>> and replace.
I can't remember what
the character
was...possibly a
>> '#' or a
space?
>>
>> ##DEF
CO2_EMS_FOR_ZONES[mmZone]
>>
>
>
!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
>> !EMS for
Damper Control by CO2
Level
>> !*****THIS
FILE IS USED TO
GENERATE A FILE THAT
HAS "" THAT NEED TO
>> BE
REMOVED******!
>>
>
>
!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
>> ! CC =
CurrentCO2Concentration
>> ! CCSP =
CurrentCO2SP
>> ! CDP =
CurrentDamperPos
>> ! CO2SPUL =
CO2_SP_Sensor UPPER
LIMIT
>> ! CO2SPLL =
CO2_SP_Sensor LOWER
LIMIT
>> ! ODACO2SPUL
= ODA CO2_SP_Sensor
>> ! ZDCS =
ZDC_Sensor
>> ! ZDC =
Zone_Damper_Changer
>> ! MDF =
MINDAMPERFRACTION
>> ! CMM =
CO2ModificationManager
>> ! CMMPr =
CO2ModificationManager
Program
>> ! CS =
CO2_Sensor
>> ! DaLL =
Damper Lower Limit
>>
>>
EnergyManagementSystem:GlobalVariable,
>> #[mmZone //
_CC] ,
>> #[mmZone //
_CCSP ] ,
>> #[mmZone //
_CDP ] ,
>> #[mmZone //
_dDamper ] ,
>> #[mmZone //
_dCO2 ] ,
>> #[mmZone //
_MM ] ,
>> #[mmZone //
_ODACO2SPULV ],
>> #[mmZone //
_CO2SPULV ],
>> #[mmZone //
_CO2SPLLV ],
>> #[mmZone //
_DaLLV ]; !- Erl
Variable 2 Name
>>
>>
EnergyManagementSystem:Sensor,
>> #[mmZone //
_CS] , ! Sensor
Name...reporting
temperature
>> mmZone ,!
Output:Variable or
Output:Meter Index Key
Name
>>
Output:Variable,*,Outdoor
Dry Bulb,hourly; !-
Zone Average [C]
>> Zone Air
Carbon Dioxide
Concentration ; !
Output:Variable or
>> Output:Meter
Name
>>
>>
EnergyManagementSystem:Sensor,
>> #[mmZone //
_ODACO2SPUL] , !
Sensor
Name...reporting
temperature
>> Outdoor CO2
Schedule , !
Output:Variable or
Output:Meter Index Key
>> Name Zone/Sys
Thermostat Cooling
Setpoint
Output:Variable,*,Zone/Sys
>> Thermostat
Cooling
Setpoint,hourly; !-
Zone Average [C]
>> Schedule
Value ; !
Output:Variable or
Output:Meter Name
>>
>> !Setpoint
Value
>>
EnergyManagementSystem:Sensor,
>> #[mmZone //
_CO2SPLL] , ! Sensor
Name...reporting
schedule
>> properties
>> CO2SPLL , !
Output:Variable or
Output:Meter Index Key
Name Zone/Sys
>> Thermostat
Cooling Setpoint
Output:Variable,*,Zone/Sys
Thermostat
>> Cooling
Setpoint,hourly; !-
Zone Average [C]
>> Schedule
Value ; !
Output:Variable or
Output:Meter Name
>>
>> !Setpoint
Value
>>
EnergyManagementSystem:Sensor,
>> #[mmZone //
_CO2SPUL] , ! Sensor
Name...reporting
schedule
>> properties
>> CO2SPUL , !
Output:Variable or
Output:Meter Index Key
Name Zone/Sys
>> Thermostat
Cooling Setpoint
Output:Variable,*,Zone/Sys
Thermostat
>> Cooling
Setpoint,hourly; !-
Zone Average [C]
>> Schedule
Value ; !
Output:Variable or
Output:Meter Name
>>
>>
EnergyManagementSystem:Sensor,
>> #[mmZone //
_DaLL] , !- Name
>> DaLL , !
Output:Variable or
Output:Meter Index Key
Name...in this
>> case
!-EnergyManagementSystem:Actuator
Available,COOLING SP
>>
SCH,Schedule:Compact,Schedule
Value,[ ]
>> Schedule
Value ;!Damper Lower
Limit Schedule
>>
>>
EnergyManagementSystem:Sensor,
>> #[mmZone //
_ZDCS] , !- Name
>> mmZone MDF ,
! Output:Variable or
Output:Meter Index Key
Name...in
>> this case
!-EnergyManagementSystem:Actuator
Available,COOLING SP
>>
SCH,Schedule:Compact,Schedule
Value,[ ]
>> Schedule
Value ;!VAV Terminal
Damper Position ; !
Output:Variable
>> or
Output:Meter Name
>>
>> ! , Component
Unique Name, Component
Type, Control Type, Units
>>
!EnergyManagementSystem:Actuator
>>
Available,MDF,Schedule:Compact,Schedule
Value,[ ]
>>
EnergyManagementSystem:Actuator,
>> #[mmZone //
_ZDC] , !- Name
>> mmZone MDF ,
!- Actuated Component
Unique Name...in this
case
>>
!-EnergyManagementSystem:Actuator
Available,COOLING SP
>>
SCH,Schedule:Compact,Schedule
Value,[ ]
>>
Schedule:Compact, !-
Actuated Component
Type
>> Schedule
Value ; !- Actuated
Component Control Type
>>
>> !***Program
Calling Proceedure***
>>
EnergyManagementSystem:ProgramCallingManager,
>> #[mmZone //
_CMM] , ! Name
>>
AfterPredictorAfterHVACManagers,!BeginTimestepBeforePredictor
, !
>> EnergyPlus
Model Calling Point
>> #[mmZone //
_CMMPr] ; ! Program 1
Name
>>
>> !***Main
Program***
>>
!******************
>>
EnergyManagementSystem:Program,
>> #[mmZone //
_CMMPr] , ! Program 1
Name
>> SET #[mmZone
// _ODACO2SPULV ] =
#[mmZone //
_ODACO2SPUL],
>> SET #[mmZone
// _CO2SPULV ] =
#[mmZone // _CO2SPUL],
>> SET #[mmZone
// _CO2SPLLV ] =
#[mmZone // _CO2SPLL],
>> SET #[mmZone
// _DaLLV ] = #[mmZone
// _DaLL] ,
>> SET #[mmZone
// _CC] = #[mmZone //
_CS] ,
>> SET #[mmZone
// _CDP] = #[mmZone //
_ZDCS] ,
>> SET #[mmZone
// _dDamper ] = (1 -
#[mmZone // _DaLLV ]),
!max min
>> damper
positions
>> SET #[mmZone
// _dCO2 ] = #[mmZone
// _CO2SPULV] -
#[mmZone //
>> _CO2SPLLV] ,
!max min CO2 levels,
i.e. SP and ODA CO2
>> SET #[mmZone
// _MM ] = 1 -
(#[mmZone // _dDamper
] / #[mmZone //
>> _dCO2 ] *
#[mmZone // _CO2SPULV]
) ,
>>
>> IF (#[mmZone
// _CC] >= #[mmZone
// _CO2SPLLV ] )
&& (#[mmZone
//
>> _CC] #[mmZone
// _CO2SPULV ] ,
>> SET #[mmZone
// _ZDC] = 1 ,
>> ENDIF;
>>
>> !***End Main
Program***
>>
!**********************
>> ##EndDEF
>>
CO2_EMS_FOR_ZONES
[U12]
>>
CO2_EMS_FOR_ZONES
[PE00WN]
>>
CO2_EMS_FOR_ZONES
[PE00WS]
>>
CO2_EMS_FOR_ZONES
[PE00WW]
>>
CO2_EMS_FOR_ZONES
[PE0Z02W]
>>
CO2_EMS_FOR_ZONES
[PE03W]
>>
CO2_EMS_FOR_ZONES
[HE00]
>>
CO2_EMS_FOR_ZONES
[HE0Z03]
>>
CO2_EMS_FOR_ZONES
[PavN]
>>
CO2_EMS_FOR_ZONES
[PavS]
>>
>>
!*******************************************DEFINE
DAMPER SCHEDULES
>> FOR
ZONES*****************************
>> ##def
DAMPER_SCH_ZONES[mmZone]
>>
>>
Schedule:Compact,
>> mmZone MDF,
>> Fraction,
>> Through:
12/31,
>> For: AllDays,
>> Until: 05:00,
0.3,!0,
>> Until: 23:00,
0.7,
>> Until: 24:00,
0.3;
>>
>> ##EndDef
>>
>>
DAMPER_SCH_ZONES [U12]
>>
DAMPER_SCH_ZONES
[PE00WN]
>>
DAMPER_SCH_ZONES
[PE00WS]
>>
DAMPER_SCH_ZONES
[PE00WW]
>>
DAMPER_SCH_ZONES
[PE0Z02W]
>>
DAMPER_SCH_ZONES
[PE03W]
>>
DAMPER_SCH_ZONES
[HE00]
>>
DAMPER_SCH_ZONES
[HE0Z03]
>>
DAMPER_SCH_ZONES
[PavN]
>>
DAMPER_SCH_ZONES
[PavS]
>>
!*******************************************END
DEFINE DAMPER
>> SCHEDULES FOR
ZONES
**********************
>
>
>
> Links:
> ------
> [1] http://www.cleantechanalytics.com
> [2] mailto: jeannieboef@xxxxxxxxx
> [3] http://energyplus.helpserve.com
> [4] http://www.energyplus.gov
> [5] http://groups.yahoo.com/group/EnergyPlus_Support/
> [6]
>
> http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmNzFiZ3NhBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzMzY5NDkxODQ-
> [7]
>
> mailto: EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=EmailDelivery:Digest
> [8]
>
> http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkYnN0NGdsBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzM2OTQ5MTg0
> [9] http://docs.yahoo.com/info/terms/
> [10]
>
> mailto: EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___
|