** Warning ** Output:PreprocessorMessage="ExpandObjects" has the following Warning conditions:
** ~~~ ** The value ConstantFlow is not a valid choice for object:
** ~~~ ** HVACTemplate:Plant:ChilledWaterLoop with the name: Chilled water loop and
** ~~~ ** field: Chilled Water Pump Configuration
************* Beginning Zone Sizing Calculations
** Warning ** Site:GroundTemperature:BuildingSurface: Some values fall outside the range of 15-25C.
** ~~~ ** These values may be inappropriate. Please consult the Input Output Reference for more details.
** Warning ** Calculated design cooling load for zone=EXISTINGWORKSHOP:ZONE1 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
************* Beginning Plant Sizing Calculations
** Warning ** In calculating the design coil UA for Coil:Cooling:Water NEWWAREHOUSE:ZONE1 COOLING COIL
** ~~~ ** the apparatus dew-point is below the coil design inlet water temperature;
** ~~~ ** the coil outlet design conditions will be changed to correct the problem.
** ~~~ ** The initial design conditions are: Tair,in = 25.4717
** ~~~ ** Wair,in = 1.093345E-002
** ~~~ ** Twater,in = 7.2200
** ~~~ ** Tair,out = 14.0000
** ~~~ ** Wair,out = 8.000000E-003
** ~~~ ** The revised design conditions are: Tair,out = 12.6116
** ~~~ ** Wair,out = 8.560853E-003
** Warning ** The design coil load is zero for Coil:Cooling:Water EXISTINGWORKSHOP:ZONE1 COOLING COIL
** ~~~ ** The autosize value for max water flow rate is zero
** Warning ** Chiller:Electric:EIR = DOE-2 CENTRIFUGAL/5.50COP: Integrated Part Load Value (IPLV) cannot be calculated.
** ~~~ ** Check limits in Cooling Capacity Function of Temperature Curve , Curve Type = BIQUADRATIC, Curve Name = DOE-2 CENTRIFUGAL/5.50COP COOLINGCAPACITY DOE-2 CENTRIFUGAL/5.50COP CAPFT
** ~~~ ** Check limits in EIR Function of Temperature Curve, Curve Type = BIQUADRATIC, Curve Name = DOE-2 CENTRIFUGAL/5.50COP ENERGYINPUTRATIO DOE-2 CENTRIFUGAL/5.50COP EIRFT
************* Testing Individual Branch Integrity
************* All Branches passed integrity testing
************* Testing Individual Supply Air Path Integrity
************* All Supply Air Paths passed integrity testing
************* Testing Individual Return Air Path Integrity
************* All Return Air Paths passed integrity testing
************* No node connection errors were found.
************* Beginning Simulation
** Warning ** ControlCompOutput: Maximum iterations exceeded for ZoneHVAC:FourPipeFanCoil = EXISTINGWORKSHOP:ZONE1 FAN COIL
** ~~~ ** ... Load met = -115.50579 W.
** ~~~ ** ... Load requested = -115.29693 W.
** ~~~ ** ... Error = 0.18114984 %.
** ~~~ ** ... Tolerance = 0.10000000 %.
** ~~~ ** ... Error = (Load met - Load requested) / MAXIMUM(Load requested, 100)